thermostatic trap testing
John Shea
Member Posts: 247
Due to the limited condensate produced by a few 3/4 fittings & nipples, I'm having a hard time determining the bad from good.
Some of the traps are closing on steam, however, after a minute or two, no condensate is relieved. Other traps will periodically let out a few drops in succession.
Is it possible that the condensate has to 'build up' to a point high enough (maybe all the way to the bellows) in order for the bellows to cool/trap to open?
Some of them are a no brainer, others seem marginal.
I plan on watching one for a full heating cycle to see if the trap ever opens for condensate.
Thanks for your help.
Some of the traps are closing on steam, however, after a minute or two, no condensate is relieved. Other traps will periodically let out a few drops in succession.
Is it possible that the condensate has to 'build up' to a point high enough (maybe all the way to the bellows) in order for the bellows to cool/trap to open?
Some of them are a no brainer, others seem marginal.
I plan on watching one for a full heating cycle to see if the trap ever opens for condensate.
Thanks for your help.
0
Comments
-
Try adding some more pipe
as a "cooling leg" to produce some condensate for the trap to work with. This is a Dead Men's trick that still works well. You still see them on thermostatic traps used to drip piping in 2-pipe steam systems.
There's a photo of a cooling leg on page 123 of Lost Art.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
trap testing
if possible, pipe a supply water prior to the trap with appropriate ball valves, back flow preventers and check valves. then you'll be able to cycle the trap and watch it function0 -
There are
some variables involved with output. The bellows are basicly throttling depending on those variables.
Delta,
Back Pressure,
Hydraulic Pressure,
In a perfect situation the trap will not allow total release of condensate during loading.0 -
supply water
tptunstall,
piped in a fresh water supply (hot) with check valve and it works like a charm. There's no longer any question as to whether the traps are good or bad. Nice to finally know for sure.
Thanks for your help.0 -
Or dunk a portion of the pipe leading to the trap in water to condense more steam in that area....
Probably a little simpler than getting a hot water source depending on how much you use the setup and how elaborate you want to get.
Matt0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements