thermostatic trap testing

John Shea
John Shea Member Posts: 247
Due to the limited condensate produced by a few 3/4 fittings & nipples, I'm having a hard time determining the bad from good.

Some of the traps are closing on steam, however, after a minute or two, no condensate is relieved. Other traps will periodically let out a few drops in succession.

Is it possible that the condensate has to 'build up' to a point high enough (maybe all the way to the bellows) in order for the bellows to cool/trap to open?

Some of them are a no brainer, others seem marginal.

I plan on watching one for a full heating cycle to see if the trap ever opens for condensate.

Thanks for your help.

Comments

  • Steamhead
    Steamhead Member Posts: 17,387
    Try adding some more pipe

    as a "cooling leg" to produce some condensate for the trap to work with. This is a Dead Men's trick that still works well. You still see them on thermostatic traps used to drip piping in 2-pipe steam systems.

    There's a photo of a cooling leg on page 123 of Lost Art.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Robert O'Connor_3
    Robert O'Connor_3 Member Posts: 272
    trap testing

    if possible, pipe a supply water prior to the trap with appropriate ball valves, back flow preventers and check valves. then you'll be able to cycle the trap and watch it function
  • Bob_19
    Bob_19 Member Posts: 94
    There are

    some variables involved with output. The bellows are basicly throttling depending on those variables.
    Delta,
    Back Pressure,
    Hydraulic Pressure,

    In a perfect situation the trap will not allow total release of condensate during loading.
  • John Shea
    John Shea Member Posts: 247
    supply water

    tptunstall,

    piped in a fresh water supply (hot) with check valve and it works like a charm. There's no longer any question as to whether the traps are good or bad. Nice to finally know for sure.

    Thanks for your help.
  • Matt Undy
    Matt Undy Member Posts: 256


    Or dunk a portion of the pipe leading to the trap in water to condense more steam in that area....

    Probably a little simpler than getting a hot water source depending on how much you use the setup and how elaborate you want to get.

    Matt