I already have a decent plan of atack to correct this condo complex noise problem. Eq. install boiler feed system, insulate main,install heder and pipe equalizer off the end any other input would be greatly appricieated.
thanks jim murtaugh

Comments

  • don_52
    don_52 Member Posts: 199
    that oak park problem...

    Jim,

    >install header and pipe equalizer.

    from the photo, yeah, looks kinda iffy.

    >install boiler feed system.

    appears as if they were thinkin about doing
    that and didn't, for what reason, who knows.
    is that red valve a flow control or just
    isolation? at any rate condesate is prolly
    backing up causing that hammer, think so?
    ( snipped weil's detail, looks familiar don't it )

    >insulate main

    indeed!

    throw in your "designed for service" valve set
    ( always worth the extra $ ) and their problems
    may disappear as if by magic.

    may not even have to re-pitch anything upstream,
    ( maybe ) but don't know that yet?

    a shame they didn't find you sooner!

    keep us posted;

    regards, don
  • RonWHC
    RonWHC Member Posts: 232
    Here goes.

    Looks like most of the distribution piping was thought up on the spot. Weil spends a lot of time & money on I&O Manuals. This one makes that look like a waste.

    Before you put in a feed water tank: what is the "A" Dimension? If it is 28" or higher, take out the improperly piped false water line & hook it up as a gravity job. Might want to pull that plug valve out of the return, too.

    A properly sized & installed header & equalizer is a must. Might be best to take one step at a time. Good luck.

  • jim murtaugh
    jim murtaugh Member Posts: 72
    WEIL

    "A" demension seems fine planed on taking out that plug valve weil also recomends feed system. i suspect the previous boiler was a big national with a big water chest
  • RonWHC
    RonWHC Member Posts: 232
    We have taken

    out 5 feed water/condensate units on Weils over the last few years & piped them gravity. The tanks/pumps were there to compensate for improperly installed or grossly oversized boilers.

    Don't know the regs in your area, but in ours, that pump triggers a mandatory daily check by a stationary steam engineer. Why not try the simple solutions first?
  • Dave Meers
    Dave Meers Member Posts: 103
    just viewed the pics

    Hi Jim,

    The near boiler piping is a mess. The supply riser looks too small out of the boiler. The loop on the return is puzzling, what were they trying to do? The plug valve in the return is a bad thing, get rid of that. Don't know if the boiler feed system is necessary. Are you having flooding problems?

    I like to fix what I know is wrong first, and go on from there, one step at a time. I don't know if the owner will like that idea, but why do more than is required.

    My advise is to change the near boiler piping to Weil's specs and clean up the return line. Skim or chemically clean the boiler water and see where you are at. These are all necessary, so you're not wasting your time or the owner's money. It also might be all that is needed.

    Keep me posted. Feel free to contact me with any questions.

    Best regards, Pat
  • Dave Meers
    Dave Meers Member Posts: 103
    question

    Hi Ron,

    What area are you from? I'm not aware of this regulation. I can see why someone would think long and hard before bringing this type of regulation into their boiler room.

    Best regards, Pat
  • jim murtaugh
    jim murtaugh Member Posts: 72
    near boiler pipe

    the install instructions say that 4" is ok but that 4" goes into a 6" main after the equalizer my thoughts while correcting equalizer and installing a header make it 6" ( wich is the boiler taping) in order to slow velocity and help that steam dry out. any thoughts anyone.thanks in advance jim murtaugh
  • Blackoakbob
    Blackoakbob Member Posts: 252
    the plug valve....

    may be less expensive than a good quality gate valve to valve off the boiler and blowout the crud build up in the return, it looks like a good place for a drop header setup for the near boiler piping. Changing the "simple" things would be better in the long run than adding a condensate pump set, float controls, make up water soleniod, etc. more mechanical parts .. more troubles. Also, your comment about a smaller steam chest leads me to a couple of thoughts... #1 the correct size (Gpm) of condensate pump to maintain proper water level on startup and #2 the adequate sized condensate tank to collect and hold returning used steam during and after the heating cycle. Just some things to consider.
    Best Regards,
  • patrick linhardt
    patrick linhardt Member Posts: 134
    that's more like it

    Hi Jim,

    I think it is an excellent idea to go "full size" from the LGB 6" supply tapping to the existing header. This will slow velocity and by theory, have drier steam leave the boiler and maintain a steadier waterline.

    Best regards, Pat
  • Patrick.

    I've been away from the 'puter for a couple days. Work in Washington, D. C.

    The requirement for a Stationary Engineer/daily check for all pumped condensate boilers has been a requirement since the Army Corp of Engineers ruled the roost. Boiler size does not matter. The pump is the trigger. Fine is $500. p/day.
  • jim murtaugh
    jim murtaugh Member Posts: 72
    lgb-8

    i belive this is only required if there isnt a low water c/o or city water feed line
  • Jim.

    The requirement here is in addition to all of the other local codes & CSD-1. Your LGB-8 would require 2 LWCO (1 testable w/ manual reset)& Manual Reset Safety Limit Pressuretrol that is wired directly to fuel valve circuit, not thru the limit.

    Funny thing is, the school engineers can't keep their boilers from becoming glowing piles of slag.


  • Dave Meers
    Dave Meers Member Posts: 103
    thanks for the info

    Hi Ron,

    Does this apply to the District of Columbia only, or the states of Maryland or Virginia? Thanks for the information.

    Best regards, Pat
  • Dave Meers
    Dave Meers Member Posts: 103
    thanks

    Hi Jim,

    I did some calculations on the velocity. At start-up the 4" causes a velocity of 59 feet per second. I don't like anything over 50 myself. I think Weil is cutting this pipe size on this boiler too close. If you pipe it in 6" the velocity slows to 26 feet per second. Nice and slow, just like the oldtimers wanted.

    On a personal note, thank you for purchasing the field guide. You should be receiving it by Wednesday.

    Best regards, Pat