Loop gets hot without circ. running
Rob_5
Member Posts: 9
I have a 5 zone hot water system (circ returns & Check valves on feed)and a bedroom zone (2nd fl) seems to circulate water, getting quite warm, and neither stat nor circ is calling or on. I question the sweat check at the feed. Any help or thoughts.
Thanks, Rob
Thanks, Rob
0
Comments
-
had similar issue
I had a similar issude where the flow valve was hanging up, so I replaced it, depending on line size, it might not be that expensive. Also check boiler water temp is around 180 because sometimes I have seen very hot water be able to push open a flow valve. hope it helps0 -
Zoning with valves or circulators, and check valves?
IF zoning with circulators and check valves, you could have a check valve with system debris lodged under the weight, hindering the valves performance. If you have 1 pump, and 5 valves, its possible a valve is stuck open, and every time any zone calls for heat you heat that zone also. Unfortunately, I dont know enough about the system to successfully diagnose the problem. Is this a new problem? Have you made any changes to the system? Is it primary, secondary piping, or supply, and return manifolds?
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
may need 2
Gravity water heat works pretty well. First step as other posts suggested, simple and cheap, is to open up the first check valve and make sure it's clean and dropping close, a few wrapps of solid solder helps with the drop. If that doesn't do it then a second check valve should be added, so they'll be one on the supply and return, to prevent this gravity heat.0 -
spring checks on both ends....
get rid of the old cast iron check and put in a taco 00xxIFC pump at one end and an inline springcheck at the other end you will loose very little active flow
cooler-denser-heavier water will drop right through warmer-lighter water - even happens in a single 1/2 inch pipe - which is why homes where all pipes are pinched to a single point drain, rarely have a freezing problem if the drain point is in a warm room
0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 93 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements