Radiator Valves open and close during heating cycle
Kevin_25
Member Posts: 5
I have replaced all main and radiator valves over the past 3 months in a one pipe steam system but during the heating cycle the valves close and then open to let a burst of steam out and close again within seconds. I have verified my pressuretrol has a cut-in 0.5 and differential of 1 but I never notice any reading on the pressure gauge on the bottom of the pigtail. The pigtail and gauge were both replaced this fall, could they be clogged already? I do drain out the returns weekly. I have also noticed that valves which have replaced have bocome fowled. Help! I'm getting tired of being woken up each morning by the clicking and hissing.
0
Comments
-
what is...
the quality of the water in the boiler/system? If it is dirty it can cause all kinds of problems....kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
quality of water
Water runs clean in seconds from the return pipes. Gauge glass is clear.0 -
An oversized boiler
can cause this. Check the Net rating of your boiler against the actual amount of radiation. For radiator ratings, get Dan's book "E.D.R.". If you have anyhting that's not in there, post again and we'll see what we can do.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.1K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 85 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 62 Pipe Deterioration
- 905 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.7K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements