One pipe steam system, radiators on the lower level are shooting water out of the air valves. It's like a bad water fountain.

Here's what I've noticed.

1.) No installation on the condensate lines or the main steam pipes.

2.) The air vents are ok, the radiators do warm after the initial knocking and beating.

3.) I can hear the air coming out.

4.) Some of the radiators pant.

5.) The water level itself is ok on the boiler.

Here's my attack plan.

1.) Insulate the pipes.
2.) Swap out the main line air vents with bigger ones.

What else do I look at? At what point do I call someone?

Comments

  • Show us a picture

    Maybe a half a dozen. Show the ends of the radiators where the valves and vents are. Show us the boiler piping from lot's of angles.

    We won't be shy.

    Noel
  • Dave_12
    Dave_12 Member Posts: 77
    SUGGESTION

    MAKE SURE THAT THE STEAM PRESSURE IS LOW, BETWEEN 0.5 PSI AND 1.5 PSI. YOU MAY BE OPERATING AT TOO HIGH A STEAM PRESSURE AND BACKING WATER UP TO THE LOWER FLOORS.
  • Steamhead
    Steamhead Member Posts: 17,380
    Also

    see that the radiator shutoff valves are completely open. If partially closed, water can back up in the radiators, which will cause spitting.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • bb
    bb Member Posts: 99
    check

    Steam Problems? here on the wall for 1 pipe steam...

    Also, make sure piping and rads are pitched back to supply.