Too many feet of baseboard?
Ted Robinson
Member Posts: 126
This continues from a few days ago. New construction of a three family building. Each floor has about 56 feet of baseboard connected in what appears to a be a single loop. Is this excessive for 1/2 inch plastic distribution pipe? Will the temp drop be too great for enough heat in the rooms furthest from the supply end?
0
Comments
-
Sure is
the limit for 3/4" supply pipe is just over 60 feet of baseboard.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
1/2" is good for abt. 1.5 gpm or 15,000 btu about 25-30 feet depending on your baseboard rating and water temperature0 -
Thanks for the help & information.0 -
When is 56 feet of baseboard too much?
When using 1/2" pipe if the total length of pipe is too much. I'm assuming the baseboard is 3/4" pipe, and the supply piping is 1/2", so we need to know how many lineal feet of pipe to calculate the pressure drop. If the head and velocity are acceptable then you can size the pump. Maximum flow through 1/2" pipe is approximately 3 gpm which is close to 3.4 gpm required to satisfy the load. But what about the system curve? Can the pump deliver it without exceeding the 4 ft per second velocity? You can still make it work regardless, but the flow might not be 100%.
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
Sorry but I don't agree. 1/2 " is good for about 1.5 gpm. 3/4 is good for about 4. Most people in the industry size for a resistance of 4'/100 feet of pipe. Based on a 20 degree TD which is standard 1/2"=15,000 btu/hr and 3/4 is 40,000 btu/hr. Select the pipe size based on the btu requirement you need and then devide the btu requirement by the rating of btu/ foot that your baseboard requires. Most residential baseboard is in the range of 400-700 btu/foot depending on your average water temperature.
Ed0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements