pressuretrol
RoosterBoy
Member Posts: 459
weil mclain 400,000 btu. 2 main runs 90' and 60' with hoffman #75 at each end. boiler stopped firing. I increased cut in from 2 to 3 (differential is at 2) so that means now cut out is 5. boiler works fine now and some radiators on 3rd floor now are heating. I've got 3 gorton #2's on order to add to the end of the mains (2 for 90 and 1 for 60). when I add these gortons can I decrease preussuretrol? thanks
lowering your pressuretrol settings
should be done now. Dan's book explains why and gives a wealth of info on how to maximize your system. WELL worth the money.0
- 87.2K THE MAIN WALL
- 118 Chimneys & Flues
- 114 Geothermal
- 164 Indoor-Air Quality
- 73 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.6K Strictly Steam
- 49 Job Opportunities