Outdoor reset and two zone constant circulation

JDemme
Member Posts: 10
How do I accomplish two zone constant circulation? I will be using a Munchkin Vision 1.
As I mentioned in another thread, I am worried about the upstairs in my open floorplan home overheating.
As I mentioned in another thread, I am worried about the upstairs in my open floorplan home overheating.
0
Comments
-
Thermostat
Put a room thermostat on the second floor, shut the pump off if the room gets too warm, No?0 -
Mixing
Add a 3-way mixing valve with it's own reset curve for the upstairs.
-Andrew0 -
the only true way to get ....
...continuous circulation in two zones, is when you use Motorized Mixing for each zone with outdoor Reset and Indoor Temperature Feedback. Balancing could achieve this too, technically. However, if the conditions for each zone vary (solar or other heat gain inflicted not permanently with the same rate) then Indoor Feedback really is the only answer.
Hope this helps,
Regards,
Mike0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 948 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements