Effect of Warm Wall on Thermostat
too hot in cold
Member Posts: 15
How much is a thermostat affected by the temp. of the wall it is on?
I found that there is a return pipe from one of my radiator zones running in the wall almost directly behind my kitchen thermostat. There is a speaker volume control mounted in an outlet box below the thermostat. I think this box must be touching the pipe. The sheetrock just above this box is 74 - 78 degrees, depending on the weather. A few feet above or below it is cooler. A foot or so to the side the wall is 72 or 73.
My kitchen has radiant heat and in very cold weather the area near the windows is 67 when the thermostat reads 71. Now I am thinking that the thermostat is warmed by that pipe in the wall. I am thinking of moving the thermostat over to the next bay, which does not contain a pipe. Do you think this will help?
I found that there is a return pipe from one of my radiator zones running in the wall almost directly behind my kitchen thermostat. There is a speaker volume control mounted in an outlet box below the thermostat. I think this box must be touching the pipe. The sheetrock just above this box is 74 - 78 degrees, depending on the weather. A few feet above or below it is cooler. A foot or so to the side the wall is 72 or 73.
My kitchen has radiant heat and in very cold weather the area near the windows is 67 when the thermostat reads 71. Now I am thinking that the thermostat is warmed by that pipe in the wall. I am thinking of moving the thermostat over to the next bay, which does not contain a pipe. Do you think this will help?
0
Comments
-
Absolutely
Yes,move it!0 -
move it
your t-stat is being lied to. If it isn't reading the proper ambeient air temp it can't work accurately.0 -
Your stat is being \"confused\"...
Usually, it's the stat sensing wall cavity temp, so the cure is to plug the wire hole with insulation. In your case, move the stat to an inside wall, away from any heat emitters and out of the sun. The themistors used on many of the more modern stats are extremely sensitive, and will respond to any variation in temperature very quickly.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements