Pump sizing question?
Jamie_6
Member Posts: 710
Would someone help me size this pump please?
Total btu's: 15,410
Flowrate: 3.1
Head loss: 11.7
Required temp. to slab 90 degrees
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Total btu's: 15,410
Flowrate: 3.1
Head loss: 11.7
Required temp. to slab 90 degrees
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
A Grundfos UPS15-42F on speed two would be real close and if you ended up needing more flow or your head was higher than you thought you could go to speed three.
hope this helps.
S Davis
Apex Radiant Heating0 -
UPS15-42F
Yes , and I picked one up this last week so as far as I know they are still available.
S Davis
Apex Radiant Heating0 -
is there still a 3spd 15-42?
i thought is was only the 15-58fc "superbrute II" now.
but the old file grundfospumps60hz has it - so i dont know - i thought when they moved the plant from germany to fresno,ca they changed the 42 to one speed only, their web site is so confusing ;(0 -
On speed two that pump is larger then a 007 correct?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
dang, or shoud i say \"ups\", my dealer is holding out on me
0 -
more like different....
cause afer the 007, taco goes off in a very different direction than grundfos
look as the pumps curves in the attached 007.pdf with the one i attached above - they do lots of head with the 009 or lots of flow with the others
while the grundfos just happens for give you a better match the 007 might just be close enough, if you have a spare 007, i would try it first0 -
there is a 007 on there know and it is not cutting it. If we close two loops the slab will atrt to warm!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
you might need speed 3 on UPS15-42xx see pic....
the 11ft of head is closer to the middle of the pump curve than it is on 2 - and we try to operate pumps in the "knee" of their curves - usually the middle third -
you can also use a 008 or even better a 009 which almost matches the flow and head you gave up front while we love to help, on something simple like this, I cant understand why your dealer isnt giving you the time of day, they get free evening seminars with dinner on this stuff and they can even bring their spouses and make it a night - manufacture's reps spend good money on this Im thinking, maybe he dont have the right stuff in stock!!!
0 -
Taco 007-F5-IFC
Attached is the submittal data information for the 007 which will give you the dimensional, and operational Characteristics.
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements