Ultra 230

Sweet_2
Member Posts: 143
Looking over installation man. On the Boiler loop, the weighted check valve that there calling for will a B@G check-Trol work as well?? If so will it be OK on the outlet of pump on the return side or does it need to be where manual wants it on the outlet side of boiler? Thanks
0
Comments
-
You can do that ...
it will work just fine.....just make sure with the 230 that u use at least 1-1/4" piping...1-1/2" is better....
Floyd0