Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Ultra 230
Sweet_2
Member Posts: 143
Looking over installation man. On the Boiler loop, the weighted check valve that there calling for will a B@G check-Trol work as well?? If so will it be OK on the outlet of pump on the return side or does it need to be where manual wants it on the outlet side of boiler? Thanks
0
Comments
-
You can do that ...
it will work just fine.....just make sure with the 230 that u use at least 1-1/4" piping...1-1/2" is better....
Floyd0
This discussion has been closed.
Categories
- All Categories
- 86.1K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 98 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 62 Pipe Deterioration
- 907 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements