NEW HYDRONIC BOILER
Options
KENG
Member Posts: 1
I am planning to replace my gas fired hot water system (150,000 BTU- Utica)with a new boiler. Most of the package boilers come with one pump attached. I have three zones. Is it better to remove the pump and put in a seperate pump for each zone or should I just use control valves?
0
Comments
-
On a smaller house a single circulator on the supply side of the boiler, downstream of [pumping away from] the point where the expansion tank takes off, works fine. Have a nice manifold with three zone valves. Get Dan Holohan's small useful book "Pumping Away".0 -
KENG.
How did you arrive at that 150,000 BTU figure? Do you know the GPM needed? As Joe said, you may not need more than one. I like zoning with pumps but small zones really don't need it. Maybe you can give more info about your system and we can come up with just the right advice.
Robert O'Connor/NJ0 -
GO WITH THE BEST
Take a look at the MONITOR boiler line MZ BOILER.COM
WHAT is not to like about this awesome equipment?0 -
everyone on this site will agree that the first step in replacing any system would be to do a heat-loss calculation and size the equipment correctly--you may have an existing 150,000 btu boiler now but most boilers are grossly oversized--you may only need a 120,000 btus or even 100,000 btu ---- go with a good control strategy--outdoor reset w/a modulating gas boiler will save you so much in energy savings that the system will have a short payback0
This discussion has been closed.
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 122 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements