Zoning with condensate
Joe West
Member Posts: 7
If I have more than one zone when using condensate, do I need a seperate by-pass for each zone? Will one by-pass work for all zones?
0
Comments
-
the reason for the bypass is...
so that you dont flash 190f+ water into steam in the eye of the pump and cavitate it's impellor to death!!!
So you CAN have one supply with one bypass and two pump branches
You turn the steam all the way up, and wait for the boilers pressure-trol to cut it off,
At this point the water is the hottest its going to get,
Run both zones and wait until the boiler goes on and off again of pressure so that the zone loops are completely hot also
Now just run the zone the will give you the slowest flow and the hottest water to the pump and set the bypass until the pump supply is down to 180, recheck for other pump, and with both as your system dynamics may be different set it so that no combo of pumps gives higher than 180
!!!Lastly!!! remove the handle to the bypass valve so that nobody can mess with it and fry your pumps
You can get all this info and much more in Dans books click on red link to left
0 -
ps: you need bronze pumps for this
as iron oxide condensate sludge will just stick clog up a cast iron pump0 -
zoning with condensate
Thanks KAL0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements