chimney sizing for staged boilers sharing same
grumbug
Member Posts: 7
gentelmen
I need some hard copy on sizing flue & thinble sizing
for multiple boilers sharing common the same
Grumbug
I need some hard copy on sizing flue & thinble sizing
for multiple boilers sharing common the same
Grumbug
0
Comments
-
What Category are these
boilers? What Make and Model number are the boilers? We need to start there and then we can go on. I also need some information on the BTU input of each, chimney or vent height, lateral run (how far from chimney or vent), what is the flue size on the boilers?
What are you using the thimble for? Are you passing through combustible material?0 -
dig out your UMC
Around here in Minnesnowta chimney size is based on total BTUH and of course horizontal run can only be a certain percentage of the overall vertical height. All of that should be in you UMC. We of course have a couple of addendums because {we} in Minnesnowta are smarter than everybody else and have to do it differant0 -
chimney sizing for staged boilers sharing same
Thanks, For the reply
Here,s the facts
2 buderus G115-28 Riello F40-F3 burners 112,000.
Chimney Height 26' 8x12 flue 8" thimble, The project
Manager thinks the 8" thimble is inadaquate wants 10"
So thats why I need printed data to resolve this
Also am planning to use a true 8" crotch to tie them
together.
Grumbug0 -
is that chimney....
inside the house/build. or on the ouside/exposed side of the building. reason being the flue gasses on a buderus can be so "cold" that it will have a difficult time going up a large exterior flue. kpc0 -
NFPA54
Get a copy of the National Fuel Gas Code, it will tell you everything you need to know about flue sizing. Many mfrs reprint it in the installation instructions too.0 -
careful how you twin them in
to start Like mentioned before use the code books, second be aware of your elbows, turns, stack temperatures (because buderuses fue gasses can get low, they can condense in the flue, corrion will occor) and finally your height. You can go onto the selkirk-metalbestos website and get ideas and calculations. Also I would not twin the boilers together with pants ( I am assuming crotch as you have called it) You should run a horizontal header and twin them into the header individually. 8 inch might be fine if you have the correct height0 -
NFPA 31 limitations
No sizing charts in '31 for dual appliances common vented the way '54 does in detail. One solution would be to install a priority switch on one appliance then common vent them into one stainless liner sized for the largest single appliance. At under 1 gph and 26 ft. you're in the 5-6" liner range. I always get the boiler techies to rig the priority switches so I don't have all the poop on parts and techniques but it does work well when you have multiple appliances sharing an inadequate chimney.
Having said all that, getting some good vent rise off the top, nice smooth runs with minimal elbows helps. Manifolding is an art with some science as I'm sure Jim Davis would tell you. I'd like to hear Jim's take on this.
Always eager to learn, too.0 -
venting
Here's a link that will tell you everything you need to know. Check with your local juridiction as well.
Steve M.
http://www.hvactechsupport.com/Dwnlds/Car-Bry_Lit/GAMA.pdf0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements