richardson and boynton return line check valve
RICHARD MIGLIACCI
Member Posts: 1
I HAVE A RICHARDSON AND BOYTON VAPOR SYSTEM IN MY HOME, AT THE RETURN LINE AT THE END OF THE RADIATOR, IN THE ELBOW IS SOME KIND OF VALVE WHICH SEEMS TO HAVE FAILED. THE RADIATOR IS NOT GETTING HOT ACROSS ALL THE SECTIONS AND IS NOT HOT ENOUGH TO KEEP THE ROOM WARM. DOES ANYONE KNOW WHERE THESE VALVES CAN BE FOUND OR CAN I USE A STEAM TRAP IN PLACE OF THE OLD VALVE?
0
Comments
-
I don't know of a source for them, but
try carefully taking it apart, it may just be crudded up. Steamhead will know if you can get parts for them. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
You need to clean it
There's a curved tube running into the radiator from the elbow which acts as a water seal. In the top side of this tube is a small hole which serves as the air vent. This hole is probably plugged and if the air can't get out the steam can't get in. You can clean this with a piece of wire. No need to replace it.
See chapter 15 of "The Lost Art of Steam Heating" for more on this fitting and the system it is part of.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead
What would happen if the steel ball was missing from that union ell. What would the symptoms be?0 -
Shouldn't be a problem nowadays
the ball checks in the Richardson and O-E return ells and the "bafflers" in the Kriebel ells were there to keep any vapor in the dry returns from backing into a radiator if someone shut it off when hot. Remember, these systems were the exception to the "no steam in the dry return" rule.
Nowadays if you're running one of these systems with a Vaporstat, you shouldn't have much vapor in the dry return. So the lack of a check ball shouldn't hurt anything. If it does, see if you can find a brass or stainless steel ball that will fit.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks again
For yet another lesson Frank.0 -
Tommy Oil
Good Morning Haven't heard from you in a while
Your twin brother (therapy?)0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements