gpm

How many GPM thru old cast iron column radiators?
What is the optimum GPM to get listed btu ratings?

Comments

  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Another \"It Depends\"

    But here's an example:

    75 sq.ft. EDR cast iron radiator.

    180° average temperature (the "standard")

    Output @ 180° average = 170 btu/hr * 75 sq.ft. = 12,750 btu/hr.

    With "standard" temperature drop across the radiator (delta-t) flow requirement is:

    gpm = Btu/hr / (500 * delta-t)

    12,750 / (500 * 20)

    12,750 / 10,000

    1.275 gpm

    ----------------------------------------------

    Is this an existing system being re-worked? If so, be VERY cautious about using 180°. The radiation is generally extremely oversized and a boiler sized properly to the heat loss of the structure will most likely be utterly incapable of heating all of the radiation to 180°!
  • Chuckles_3
    Chuckles_3 Member Posts: 110


    With lower gpm there are fewer gallons passing through, but each gallon spends more time losing heat in the radiator. The output does drop a bit with lower gpm, because as the water cools in the radiator it loses less heat, but it's a rather small effect. Gravity systems did fine with very low gpm. You can use the lowest gpm that will do the job. That way you'll also get the largest delta-t which is good for a condensing boiler. Multispeed pumps are great for finding out how low you can go.