Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Just 2 psi folks, that's all!
Ross_6
Member Posts: 9
Went on a job yesterday, newer install at the fire hall.
One-pipe steam. Operating limit 6#, High limit 12#, hi-lo fire 4.5#!!!! Boiler water logged, and no heat. One main air vent for two dry returns, installed right into the tee. City's wondering why such a new system costs as much to run as the old one. Hmmmmmm....
So I reset all of the operating controls, cooking along at 1.5#. People in the field that don't know what they are doing rule! They put money in my pocket!
One-pipe steam. Operating limit 6#, High limit 12#, hi-lo fire 4.5#!!!! Boiler water logged, and no heat. One main air vent for two dry returns, installed right into the tee. City's wondering why such a new system costs as much to run as the old one. Hmmmmmm....
So I reset all of the operating controls, cooking along at 1.5#. People in the field that don't know what they are doing rule! They put money in my pocket!
0
Comments
-
Does any one know how to read?!
Went on a job yesterday, newer install at the fire hall.
One-pipe steam. Operating limit 6#, High limit 12#, hi-lo fire 4.5#!!!! Boiler water logged, and no heat. One main air vent for two dry returns, installed right into the tee. City's wondering why such a new system costs as much to run as the old one. Hmmmmmm....
So I reset all of the operating controls, cooking along at 1.5#. People in the field that don't know what they are doing rule! They put money in my pocket!0 -
Ross
I could'nt agree more0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements