Just 2 psi folks, that's all!
Ross_6
Member Posts: 9
Went on a job yesterday, newer install at the fire hall.
One-pipe steam. Operating limit 6#, High limit 12#, hi-lo fire 4.5#!!!! Boiler water logged, and no heat. One main air vent for two dry returns, installed right into the tee. City's wondering why such a new system costs as much to run as the old one. Hmmmmmm....
So I reset all of the operating controls, cooking along at 1.5#. People in the field that don't know what they are doing rule! They put money in my pocket!
One-pipe steam. Operating limit 6#, High limit 12#, hi-lo fire 4.5#!!!! Boiler water logged, and no heat. One main air vent for two dry returns, installed right into the tee. City's wondering why such a new system costs as much to run as the old one. Hmmmmmm....
So I reset all of the operating controls, cooking along at 1.5#. People in the field that don't know what they are doing rule! They put money in my pocket!
0
Comments
-
Does any one know how to read?!
Went on a job yesterday, newer install at the fire hall.
One-pipe steam. Operating limit 6#, High limit 12#, hi-lo fire 4.5#!!!! Boiler water logged, and no heat. One main air vent for two dry returns, installed right into the tee. City's wondering why such a new system costs as much to run as the old one. Hmmmmmm....
So I reset all of the operating controls, cooking along at 1.5#. People in the field that don't know what they are doing rule! They put money in my pocket!0 -
Ross
I could'nt agree more0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements