Coil heating capacity
I am working on a very old building with no drawings or nameplates on any of the equipment. I am trying to determine the approximate heating capacity of a steam coil in an air handler. I know the square foot face area of the coil, the airflow across the coil is probably 500 fpm, and the steam is at 12 psi. How can I calculate the heating capacity???
Any help would be apprecicated.
Any help would be apprecicated.
0
Comments
-
priviledged inside engineer information
call DOW equipment sales and speak to len ujazdowski 917-407-2503 he will help you select and size it free0 -
If You Know The...
...CFM being moved by the fan, then you can use:
CFM X 1.08 X delta-T in F all divided by 1000 to get lbs/hr steam required.0 -
Thanks Michal
Dave0 -
Thanks Tony,
Is 40 degree air in and 90 degree air out a good assumption?0