Coil heating capacity

I am working on a very old building with no drawings or nameplates on any of the equipment. I am trying to determine the approximate heating capacity of a steam coil in an air handler. I know the square foot face area of the coil, the airflow across the coil is probably 500 fpm, and the steam is at 12 psi. How can I calculate the heating capacity???

Any help would be apprecicated.

Comments

  • Michal_2
    Michal_2 Member Posts: 12
    priviledged inside engineer information

    call DOW equipment sales and speak to len ujazdowski 917-407-2503 he will help you select and size it free
  • Tony Conner_2
    Tony Conner_2 Member Posts: 443
    If You Know The...

    ...CFM being moved by the fan, then you can use:

    CFM X 1.08 X delta-T in F all divided by 1000 to get lbs/hr steam required.


  • Thanks Michal

    Dave


  • Thanks Tony,

    Is 40 degree air in and 90 degree air out a good assumption?