Are all hydronic guages the same?
Butch_3
Member Posts: 5
I have a question. I have 2 properties. One is a duplex with an apartment on each floor and a single family home. My question is this. Are the guages on hydronic boilers supposed to all read the same? I have 2 boilers in my duplex and I am not exactly sure what the pressure is supposed to be cold and hot. The same goes for my other boiler that is a gravity fed boiler in my other house. Do they all operate off of the same PSI? The 2 boilers in the duplex are 40k BTU's and the other one is 100000 BTU's. The assumption is that cold it will read 8lbs and hot anywhere between 20&25lbs. Is that correct? Thanks in advance for all your input.
0
Comments
-
Standard Operating Pressure
for hot water hydronic systems are between 12 and 15 psi for a 1-2 story building.
As far as taller buildings, my rule of thumb is to provide enough pressure to lift the water to the highest point in the system and have 6 psi at the top to purge air.
Hot or cold, the gauge should not move. If it does, there may be a problem with the expansion tank, i.e. ruptured bladder, incorrect fill pressure).
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements