V75
Steamhead
Member Posts: 17,387
those center-to-center measurements don't have to be spot-on, since the extra swing joints in the header will let you compensate.
I don't know about the V7 series, but in several boiler instruction sheets where the second tapping wasn't listed as mandatory, it was shown as "optional". Which to me in this case, means it's a real good idea to use the second tapping.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
I don't know about the V7 series, but in several boiler instruction sheets where the second tapping wasn't listed as mandatory, it was shown as "optional". Which to me in this case, means it's a real good idea to use the second tapping.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
Glen Stanton, et al
I have a V75, 596 MBH steamer. It is now piped with one tapping. It has two tappings. (5 sections) The book shows piping for one tapping for V73-V75, and two tappings for V76-V79. Also the 76-79 has three inch headers and mains, while the 73-75 has two inch. My two inch mains can handle the load of 503 EDR. I am planning on repiping with both tappings, (dropped header) and hopefully using 4 inch header. I know that it will work, but I wonder why the literature shows only one tapping for the V75? There is also a chart showing dimensions that includes the distance (on center) between the tappings. It starts at the V76.
It goes from 21", 25", 29". So can I assume the next smaller is 17"? It looks like it measures closer to 17.5", but I'd hafta get the jacket off to be sure. Does anyone know?
JakeThere was an error rendering this rich post.
0 -
V75 Piping
While the I&O manual states that a single riser on the V75 is optional, experience with steam tells us that two risers is a better way. Testing with one tapping has proven that the volume of steam can be adequately supplied to the system through a single riser. I always try to tell folks to use them both. It provides for a much more stable water line as well as slowing the velocity of the steam leaving the boiler down a bit. Hope this helps.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
How old is it? Might be better off waiting to see if its going to last. Might be better off getting a V80
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements