mouse turds on Munchkin HX?
R. Kalia_4
Member Posts: 18
My first year with a Munchkin T80, so I've been monitoring efficiency. Over time, nat gas usage (therms per degree-day) has increased 20%. Now the weather is the same as last November, and the Munchkin is using 20% more gas per day than in November.
I opened it up today. The HX has a large number of little loose pellets on it (see photo). They are dark gray, irregular pellets less than 1/16" in size. Some crumble when squeezed, others are quite hard.
Now I'm an amateur and I've never opened up a boiler before. (Yes, I was able to vacuum and clean and put it back together, it seems to be running fine and not leaking, although I haven't had time to measure efficiency yet.) So my question is, are these pellets normal?
Also, there is some white powder, coming from the ceramic backing. Is this normal?
I opened it up today. The HX has a large number of little loose pellets on it (see photo). They are dark gray, irregular pellets less than 1/16" in size. Some crumble when squeezed, others are quite hard.
Now I'm an amateur and I've never opened up a boiler before. (Yes, I was able to vacuum and clean and put it back together, it seems to be running fine and not leaking, although I haven't had time to measure efficiency yet.) So my question is, are these pellets normal?
Also, there is some white powder, coming from the ceramic backing. Is this normal?
0
Comments
-
Interesting that the original mouse turds thread has been completely erased after someone added a new post recently. It had useful information.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements