Michael:
Why would it be per sqft when the convector is like a BB only a bit wider? Arent they measured by feet? Linear feet?
Neil
Why would it be per sqft when the convector is like a BB only a bit wider? Arent they measured by feet? Linear feet?
Neil
0
Comments
-
Convectors Rating
I have the cast iron convectors with recessed cabinets around the house. They have 3 tubes running in between the fins. Would like to know the BTU rating per feet if I can?0 -
A good resource
Try http://www.burnham.com/pdfs/htghelper.pdf. You'll find cast-iron convectors on page 45.
You can convert from the square feet EDR to BTU using the temperature of your system. It's about 240 BTU/sqft for steam, around 170 BTU/sqft for 180 degree hot water.
-Michael0 -
Convector Ratings
Although there are some ratings in the Heating Helper, these are only representative samples of various types in the field. If what you have are actually convectors, you will need to know the depth, width and height of the cabinet as well as the number of elements installed (some have more than one tier) to properly determine the outputs. Widths and heights of the cabinet are what generally increase or decrease the outputs. Hope this helps.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
Muti Tier
I thought that can be done, I made a post a few weeks back asking if I can piggy back to increase BTU output from said convectors, but no reply.
Thanks Glenn
Neil0 -
Multi-tiering
elements in convectors does not generally increase the output very much. The reason for this has to do with the devices name. It is a convector because it convects air through itself. The element is there to heat the air as it passes through but without reducing the convection principle by any appreciable amount. Adding another tier will decrease the air flow and will only give you about 30% more output. I have never seen cast iron elements double-tiered however.They generally have legs on them to support their weight. Any twin-tiered convectors I have seen have always been copper-finned elements and the cabinets were far in excess of the normal 20" high. Hope this helps.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
Glenn
Cabinet Depth is 8 1/4", lenghth is 64 1/4" and Height is 24"
Now the # I see in the copper chart is 79.4. What next to determind the BTU output at 180*?
Thanks,
Neil0 -
Outputs
If your elements are cast iron, then the rating of that convector is 70.4 square feet. If they are copper the rating is 79.4. Either way the output in btuh will be the square footage rating multiplied by a factor of 170 btu/square foot of radiation. For the cast iron elements this will be 11,968 btuh and for copper 13,498 btuh. Hope this helps.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
Glenn S. Update
Remember my second problem was the quick drop in supply temp when the bioiler fired up? Well last night I checked it out; it is wired: the circulator only comes on when the boiler fires, when the boiler shuts down, the zone valve remains open (as per the STAT) and the circulator is off!!! So all along I thought the circ was on
Will rewire tonight. Question: In the mono flow setup that I have, with just the zone valve open and the circ off, would I have any circulation, if any, would it be sufficeint to flow through the convectors? If not, all that gravity circulation was just heating the main pipe?
Neil0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements