venting

phil henzel
Member Posts: 3
I have a large steam coil, with a modulation valve controling steam to inlet of coil, with f&t traps place down at floor level on outlet.The problem is water hammer. The traps seem to be good ,I am wondering if there sould be a vaccum breaker after the modulation valve?
0
Comments
-
You're right
When the valve closes a vacuum will form, keeping the water from draining. when steam enters and hits the water, it will bang. A vacuum breaker will solve the problem. Some vacuum breakers require a small water seal when used on steam, check the instructions to be sure.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0