Heating loop length

Paul_28
Paul_28 Member Posts: 113
What is the maximum length heating loop the can be made with ¾ inch copper pipe?

Comments

  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Like most things in hydronics the answer is, "it depends."

    But, using the below generally regarded "safe" parameters of:

    1) 20° temperature drop in the loop

    2) 1 gpm flow

    3) 170° AVERAGE water temperature (assumes 180° supply and 20° temperature drop)

    4) 480 btu/hr per foot of baseboard (65° entering air)

    --------------------------

    One gallon per minute of flow @ 20° temperature drop gives you 10,000 btu/hr to work with.

    10,000 / 480 = 20.833' of baseboard max @ 1 gpm.

    --------------------------

    With 2 gpm of flow @ 20° temperature drop you get 20,000 btu/hr to work with.

    20,000 / 480 = 41.666' of baseboard max @ 2 gpm.

    --------------------------

    With 3 gpm of flow @ 20° temperature drop you get 30,000 btu/hr to work with.

    30,000 / 480 = 62.5' of baseboard max @ 3 gpm.

    --------------------------

    With 4 gpm of flow @ 20° temperature drop you get 40,000 btu/hr to work with. 4 gpm is the the highest recommended flow rate and baseboard output can now be considered to be 510 btu/hr per foot with 4 gpm of flow.

    40,000 / 510 = 78.43' of baseboard max @ 4 gpm.

    --------------------------

    To compute flow you must first find the head loss in the loop including all fittings, etc. Then select a circulator that will move the desired amount of water at that head loss.

    --------------------------

    If you design for a 30° temperature drop in the loop (again considered near the maximum safe design level) each gallon per minute of flow will now move 15,000 btu/hr. BUT, the average temperature will now be lower at about 165° (assuming 180° supply) so each foot of baseboard will be putting out slightly less heat.
  • Paul_28
    Paul_28 Member Posts: 113
    Thank you

    > Like most things in hydronics the answer is, "it

    > depends."

    >

    > But, using the below generally

    > regarded "safe" parameters of:

    >

    > 1) 20°

    > temperature drop in the loop

    >

    > 2) 1 gpm

    > flow

    >

    > 3) 170° AVERAGE water temperature

    > (assumes 180° supply and 20° temperature

    > drop)

    >

    > 4) 480 btu/hr per foot of baseboard

    > (65° entering

    > air)

    >

    > --------------------------

    >

    > One gallon

    > per minute of flow @ 20° temperature drop gives

    > you 10,000 btu/hr to work with.

    >

    > 10,000 / 480 =

    > 20.833' of baseboard max @ 1

    > gpm.

    >

    > --------------------------

    >

    > With 2 gpm

    > of flow @ 20° temperature drop you get 20,000

    > btu/hr to work with.

    >

    > 20,000 / 480 = 41.666' of

    > baseboard max @ 2

    > gpm.

    >

    > --------------------------

    >

    > With 3 gpm

    > of flow @ 20° temperature drop you get 30,000

    > btu/hr to work with.

    >

    > 30,000 / 480 = 62.5' of

    > baseboard max @ 3

    > gpm.

    >

    > --------------------------

    >

    > With 4 gpm

    > of flow @ 20° temperature drop you get 40,000

    > btu/hr to work with. 4 gpm is the the highest

    > recommended flow rate and baseboard output can

    > now be considered to be 510 btu/hr per foot with

    > 4 gpm of flow.

    >

    > 40,000 / 510 = 78.43' of

    > baseboard max @ 4

    > gpm.

    >

    > --------------------------

    >

    > To compute

    > flow you must first find the head loss in the

    > loop including all fittings, etc. Then select a

    > circulator that will move the desired amount of

    > water at that head

    > loss.

    >

    > --------------------------

    >

    > If you

    > design for a 30° temperature drop in the loop

    > (again considered near the maximum safe design

    > level) each gallon per minute of flow will now

    > move 15,000 btu/hr. BUT, the average temperature

    > will now be lower at about 165° (assuming 180°

    > supply) so each foot of baseboard will be putting

    > out slightly less heat.