Heating loop length
Paul_28
Paul_28 Member Posts: 113
What is the maximum length heating loop the can be made with ¾ inch copper pipe?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Like most things in hydronics the answer is, "it depends."
    But, using the below generally regarded "safe" parameters of:
    1) 20° temperature drop in the loop
    2) 1 gpm flow
    3) 170° AVERAGE water temperature (assumes 180° supply and 20° temperature drop)
    4) 480 btu/hr per foot of baseboard (65° entering air)
    One gallon per minute of flow @ 20° temperature drop gives you 10,000 btu/hr to work with.
    10,000 / 480 = 20.833' of baseboard max @ 1 gpm.
    With 2 gpm of flow @ 20° temperature drop you get 20,000 btu/hr to work with.
    20,000 / 480 = 41.666' of baseboard max @ 2 gpm.
    With 3 gpm of flow @ 20° temperature drop you get 30,000 btu/hr to work with.
    30,000 / 480 = 62.5' of baseboard max @ 3 gpm.
    With 4 gpm of flow @ 20° temperature drop you get 40,000 btu/hr to work with. 4 gpm is the the highest recommended flow rate and baseboard output can now be considered to be 510 btu/hr per foot with 4 gpm of flow.
    40,000 / 510 = 78.43' of baseboard max @ 4 gpm.
    To compute flow you must first find the head loss in the loop including all fittings, etc. Then select a circulator that will move the desired amount of water at that head loss.
    If you design for a 30° temperature drop in the loop (again considered near the maximum safe design level) each gallon per minute of flow will now move 15,000 btu/hr. BUT, the average temperature will now be lower at about 165° (assuming 180° supply) so each foot of baseboard will be putting out slightly less heat.
  • Paul_28
    Thank you
    > depends."
    > 1) 20°
    > 2) 1 gpm
    > flow
    > drop)
    > (65° entering
    > air)
    > One gallon
    > 10,000 / 480 =
    > gpm.
    > With 2 gpm
    > baseboard max @ 2
    > gpm.
    > With 3 gpm
    > baseboard max @ 3
    > gpm.
    > With 4 gpm
    > 4 gpm of flow.
    > baseboard max @ 4
    > gpm.
    > To compute
    > water at that head
    > loss.
    > If you
Welcome
It looks like you're new here. Sign in or register to get started.