Dropped Header??

Steve_35
Steve_35 Member Posts: 546
It also allows for varying expansion rates between the cast iron of the boiler and the steel of the piping. The elbows become "swivel" joints.

Comments

  • tony the tech
    tony the tech Member Posts: 26
    Dropped header?

    I have read several posts referring to a dropped header on a steam boiler. I saw a post that showed a diagram from Burnham on what it should look like. My question is, other than space constraints why would you need or want a droped header? Is it all about space?
    Thanks
    Tony
  • David Sutton_5
    David Sutton_5 Member Posts: 87
    Drier Steam

    the extra flip allows for the steam to become drier before it heads out to do its job
  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688
    Drop Header??

    Here we go again!!

    Robert O'Connor/NJ
  • tony the tech
    tony the tech Member Posts: 26
    ??

    What do you mean by that?
  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688
    Anthony..

    It is a very active topic among mechanics here on the "WALL"

    Click on the search feature above and type in drop header you'll find some interesting discussion.

    Robert O'Connor/NJ
  • Steamhead
    Steamhead Member Posts: 17,375
    It's also

    much easier to put together if your boiler requires two or more risers from the boiler to the header. This is because of the two added swing joints. We drop all our headers now, as almost all the boilers we install need two risers to the header.

    Here's a shot of a Columbia gas steamer we did recently.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • jeff_51
    jeff_51 Member Posts: 545
    they were new to me untill just recently

    but after doing a replacement on a 800'000 btu steamer with a header that was too low and doing a drop header I am convinced it produces dryer steam and is certainly easier to pipe. I know from watching the water glass we are pulling water up into the risers, but after correcting the drip and with the drop headers, that system is just purring.
  • Mad Dog
    Mad Dog Member Posts: 2,595
    You are now a memeber of the...............................

    Drop-header club. Jeff. An inspector here on Long Island failed a job of Ron Jr's because he was probably not accustomed to seeing one. They rule! Mad Dog

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • jeff_51
    jeff_51 Member Posts: 545
    ya I read about Ron Jr's problem

    hadn't realized there was so much published info on drop headers and going back to the 30's I thought someone said there was boiler info on drop header going back to then. Here if Ron finally got it ok'd?