Pro Press
EJW
Member Posts: 321
I know someone asked this but I can't find the thread. Is it possible to use Pro fittings on baseboard heat? I was at a freeze up last night and could have but I didn't dare til I found out. Thanks, EJW
0
Comments
-
Not recommended...
The tubing is SUBSTANTIALLY lighter. I asked and they said no go.
It IS tempting though...
ME0 -
Pro-Press
I have done it a couple of times and no leaks yet, both times where slab with tile so if we did get a small leak there would not be any damage, and we ran it by the homowner and let them know it was not reccommended and let them make the decision.
S Davis
Apex Radiant Heating0 -
Tempting
It was tempting at 11pm last night. I was at the last split in a section that the return line doubled back under the fin tube. There were 2 splits, one on the fin and one on the M copper. I had a pocket full of Pro couplings and the temptation was there. Then I thought " I saw this question on the wall, but never went back to see the replies". I was chicken and soldered them both. Thanks for the answers. EJW0 -
Am I correct in assuming that the propress is ok on M, L, K and Not on the thin baseboard tubing??????
Ed0 -
I have used it on BB
It works great on the copper tubing of almost any thickness. No leaks and no call backs........it is all we use ....the only time we sweat is to install mixing valves or zone valves (still waiting for pp valves).........They propress leak when the copper is old and pitted inside (should be changed anyway) and if I forget to crimp a joint. (yes I have goten wet).........other than that we have used them for years with no leaks or problems......good luck and give it a try....0 -
Mellow,
We have one at work that everyone has used. We even added the 2 1/2-4" kit. It's great for computer rooms, hospitals anywhere they don't want a torch running. I know they have a battery operated one now--the electric model is heavy. Try doing 4" hanging off a ladder with that. Never had a leak yet.
Like everything else it has it's place.
Was just wondering about the thin tubing.
Ed0 -
Mellow
PP ball valves are here. Cimberio makes them but they aint cheap. 1/2 PP ready ball valve was about 16.50 dollars, 3/4 was 20.62, 1" was 21.57. I've been buying threaded bsll vavles and putting MPT adaptors in each end. 1/2 MPT adaptors are 1.30 each so if a ball valve costs 4 dollars plus 2.60 for MPT adaptorsplus 10 minutes labor, say 3.40 you've spent 10 dollars for a 1/2 inch ball valve. I'm thinking of buying several boxes of threaded ball valves and having my helper put them together in advance in the morning hours while rush hour is still bad. Make progress instead of sitting in traffic, no? WW
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
yes
we do that too. Prep the job a day ahead and you can have more time to do a quality job. We have the battery propress and it is great in tight spots but the crimp is slow on the bigger pipes...... I like to use the plug in propress when I want to crimp alot of pipe or big pipe. The other good thing about the plug in is that it will work in the cold..... The bat. style propress has to be warm to work....... I do service at night and if it is too cold it will not work. Just did another 30 feet of old bb today. Had to finsh a freeze up we started a week ago. propressed all the bb together just removing the split peaces. no leaks and I didn't have to play with fire. It is so nice.0 -
> we ran it by the homowner and let them know
> it was not reccommended and let them make the
> decision.
>
> S Davis
You must be joking??? If you knew it was not recommended, why would you let the homeowner make the decision? You are suppose to be the pro, not them.0 -
Emergency
Can you say emergency repair at 2:00 am and draining the system would have taken hours for the repair, I am also not opposed to trying to save my customers money, as long as they are aware of the pros and cons customers are capable of making their own decisions on their own homes. you must be one of the guy's that think homeowners are to stupid to think for themselves!!
S Davis
Apex Radiant Heating0 -
I was not aware
that it is not recommended.
We have used it for about ten freeze up jobs with NO PROBLEMS. Most of these jobs where done LAST YEAR .
I'll have to call Ridgid and find out the poop.
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Not to seem stupid but exactly how does this pro-press operation work? Is it some type of compression system? Is the tool needed for this pricey?0 -
The reason its not approved...
has more to do with the fittings ability to resist pull out than it is sealing capability. The PP fitting depends on the rigidity if the pipe to resist blow out. The tube used for BBR is so thin that it doesn't have a lot of resistance to blow out. As long as the system won't be seeing any high pressures, or the pipe is restrained on both ends to avoid tromboning, then I don't see any issues.
But then again, I'm NOT the manufacturer. Just a simple hot water plumber roaming the plains of Colorado...Looking for potatoes...
ME0 -
Irritated Impatient Itchy Finger Syndrome....
Sorry...
ME0 -
Thanks Mark
Out here we say Potatoes ....... wait ... ?
I am afraid we'll forget how to solder.
The times they are a changin !
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
it crimps the copper together. 2. yes sort of 3. most say yes but I have saved so much time with the propress and time is money. I have done two person jobs in the same time with just one person. cuts the time in half.....0 -
mellow do you
have to keep the whole tool warm or is just the batteries that are a problem in the cold? also, how do you like the swivel head. we have three of the plug ins and we love them. has anyone else noticed especially on the bigger sizes the pipe gets cockeyed when you crimp it.0 -
Tool temp
talked to rigid tec and he sad must be above 26 degrees it is hydrolic so the oil needs to be warm
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I have to hold it tight
to get it to crimp staight sometimes. When the tool crimps it can pull the joint and make it look bad but you can normaly bend it back. The swivel head works in spots you can't get the other tool. If you plan ahead that swivel head is not needed often but is nice to have anyway. The whole tool has to be warm for the tool to work (I know the propress gods will get me for this but I use the plug in propress in below zero temps). I kinda have to because we do not carry sweat fittings anymore. We found the propress works so well we don't want to fight with the torch.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 93 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements