Expansion Tank

I am upgrading (due to frozen burst) from a WM 68(?) to a WM WTGO 3 boiler using a 3 zone valve water system. The circulator was before boiler on the return line and I moved it to after the boiler on the supply line as recommended. The expansion tank is after the circulator on the supply line; my question is: Does the expansion tank need to also be moved? to either before the circulator or directly off the boiler

WAS: circulator > boiler > Air purger w/expansion tank and air eliminator

NOW: Boiler w/ air eliminator > circulator > Air Purger w/ expansion tank and air eliminator

Also, can the the old burner be used on the WTGO 3?

Comments

  • ed wallace
    ed wallace Member Posts: 1,613
    new boiler

    install air eliminater on the supply install expansion tank below the air eliminater attach water supply on a tee between air eliminater and expansion tank then install pump after air eliminater
  • Todd_9
    Todd_9 Member Posts: 88
    Burner selection

    It depends, if you are using the Riello or Carlin ez1 yes. If its an AFG, then you may need to change the airtube and endcone. You should also change the control to pre-post purge. I would always use a new burner that matches the specs. If not you may spend more time than its worth trying to get it right.
  • Glenn Harrison_2
    Glenn Harrison_2 Member Posts: 845
    Here's a picture of the best way to pipe it

    Compliments of Mark Eatherton
  • Frank G_2
    Frank G_2 Member Posts: 7


    Thanks for the help