Natural gas flame and CO
Jeff_17
Jeff_17 Member Posts: 99
Here is my question:
I have a steam boiler that runs on natural gas. The flames are MOSTLY blue with sketchy, intermittent, yellowish-white tips. While my cooktop burns in the kitchen, it also burns the same way. I am assuming this allows for the hottest flame. What changes the color of the flame...i.e.does more oxygen in the mix cause more yellow or more blue?
Also, does a mostly yellow flame indicate a high level of CO might be emitted?
In the olden days, they burned natural gas in homes for lighting and it burned yellow? Was there any special "mix" the fixture used or was it as simple as running gas to the fixture and adjusting the flow for light?
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    You can't just \"eyeball\" the flame...
    you must use combustion testing instruments to set up, service and check ANY combustion appliance. That's the ONLY way to know what the status of your system is.
  • Geno_15
    Geno_15 Member Posts: 158
    Ditto
    blue is the color looked for but CO can only be measured with instruments.
    I met a guy once from the midwest,{Colorado I think} who told me that out there they smelled the exhaust to tell if it's set up right, DON'T DO THIS! if the CO is high you'll find out, just hope there's someone there to call 911 cuz you'll be passed out!
  • Jeff_17
    Actually, my question is more....
    about gas lighting in an old home. When they lit their homes with gas about 100 years ago, the fixtures, whether ceiling or wall mount, burned with a yellow-white flame. What makes for the difference in color as compared to my stove/boiler? Is there an additive today...or a gas-air ratio that gives the two colors?
  • ed wallace
    ed wallace Member Posts: 1,612
    gas flame color
    more then likely 100 yrs ago the were burning coal gas that is coal that had been gasafied
  • Jeff_17
    They were...
    burning coal gas. The old plaster ceiling actually had medallions on them to collect the SOOT from the coal gas. I know that some old RESTORED Victorians in San Francisco have reinstalled the gas lighting for effect only....and their flames are more yellow than the blue we see on our burners/stove.....and they do not use coal gas.
    Maybe someone can answer this....when you install a natural gas insert in a fireplace...whether it is vent free or not...why does THAT natural gas look like a REAL, wood fire. What "makes" that natural gas flame turn the yellow/white?
  • Ted_4
    Ted_4 Member Posts: 86
    Incandescence
    The color of any incandescent light source depends on its temperature. A "yellow" flame is burning at a cooler temperature than a "blue" one. The temperature a gas flame burns is dependent on how well the fuel and air are mixed before they start to burn. The burners on modern gas appliances have mixing chambers, the old gas lights do not. The fuel type is not the determining factor. Even fuel oil can burn blue under the right conditions. Remember the old "Blue-Ray" boilers? The old GE units with air atomization burners had flames that were blue for the first couple of inches.
  • Greg_26
    Greg_26 Member Posts: 8
    Town Gas
    Not only did they burn coal gas ("Town Gas") but most, if not all, of the old gas fixtures used a cloth(?) mantle of some sort. Some also had a ceramic mantle. In 1889 a gas light was invented that pointed it's flame down instead of up to compete with those new fangled electric lights. The last coal gas plant went off-line in NY in the early 70s. Between 1850 and 1960 more than 50,000 coal gas plants operated in the US.
    There was also carbide gas (acetylene). This was invented in the late 1890s and by 1900 was becoming very a popular way to produce domestic gas, especially in Europe. Home owners would have a tank partially buried in the back yard where they would mix carbide crystals and water to produce acetylene - sometimes with explosive results. Another option was vaporized gasoline. In this case, there was a large contraption usually in the basement that would be filled with gasoline. There would be large counter weights that would have to be reset periodically like a grandfather clock. The weights would compress the gas and vaporize. There is one of these in the Smithsonian.
    By the 1890s most towns with populations of about 10,000 or more had some means to produce town gas. As the towns grew they would interconnect there piping systems with other towns. By the 20s natural gas was starting to replace coal gas as the preferred method but the two systems operated side by side for many decades.
    Greg
  • jbplumber
    jbplumber Member Posts: 89
    I was shown
    a getup in the basement of an old house and was told it was a gas generator. Not much left I recall must have been acetylene I would assume. Not some thing I would play with.
  • Sweet_2
    Sweet_2 Member Posts: 143
    Its the flame
    hitting the logs themselves. If you look at a well used set of logs in a gas log set youll see soot collecting on the logs. Incomplete combustion , take the logs out youll have a nice blue flame. Never had the pleasure of working on a vent free insert and dont think I want to, Ill have trouble sleeping.
  • Ken D.
    Ken D. Member Posts: 836
    Yellow flame
    On a properly burning gas burner, the streaks of yellow are caused by impurities in the gas and also impurities (dust) in the air. Try beating a garment or gloves or even sweeping the floor when the burner is on and you'll see. As far as a gas fireplace is concerned, the flame hitting the logs and also the small pieces of mineral wool (Which is why they are there)cause the flame to cool thus giving off yellow light. The Coleman camp lanterns use the same principle with the fabric mantles.
  • Bob Harper
    Bob Harper Member Posts: 1,181
    luminous flame
    Check out the discussion in the thread Is CO Poisonous?
    The yellow tipping is a combination things. You have incomplete combustion due to cooling flames(secondary air and impingement) and less than stoichiometric combustion mixing resulting in unoxidized carbon & trash particles glowing. There are various other compounds in this gas plume including CO2, CO, NOx, aldehydes, air,unburned fuel and water vapor. When the unburned carbon atoms attach in clumps, you get "soot". As seen under polarized light microscopy(PLM), these clusters are friable and easily disperse when pressed. Compare that to the soot from long chain alkane aliphatic hydrocarbons such as diesel fuel, heating oil, cooking oil, or candle wax. These clusters have unburned fuel attached with a yellowish matrix and the whole mess does not disperse when pressed. While PLM is usually sufficient to identify the soot source, gas chromatography with mass spectrometry or gc/ms will identify the exact compounds in the soot and therefore, its source.
  • The color that typically shows up
    in the flame from stirring up dust is "orange Streaks" they do not cause any problem.
    I can tell you that I have stayed in hotels all over the country and usually in the dining areas they have gas logs. It has become a habit of mine to carry a CO detector everywhere I go. Here is the question for the day - what do you think I have measured as CO levels in those dining areas within 10 feet to right in front of the gas logs???
    Yellow flames are usually the result of insufficent primary air, the air shutter closed, dirt in the air opening, mis aligned burners etc. There are other causes all of which should be corrected.
    A properly adjusted gas flame should be a soft stable blue flame not lifting or roaring not floating around.
    There have been burners in the past that burn yellow, such as gas lights. They typically burn yellow because they do not have a primary air opening and in fact are called yellow flame burners. Years ago a company by the name of Holoyoke made a yellow flame burner that was used to convert old oil and kerosene kitchen heating stoves to gas. They can burn yellow safely becuse they are designed with adequate clearances so that impingement does not occur.
  • jerry scharf_2
    jerry scharf_2 Member Posts: 414
    interesting
    Bob,
    thanks for the info. I had no idea about the difference in soot. How hard would it be to tell the difference in the field between the two types? There is often a "it's from candles" response to soot streaking from baseboard heaters. If you could tell the difference between types of soot in the field, it could really help this.
    Also, I'm interested in the aldahyde formation. How does it form, and what are the concequences? Do the levels here compare to the long term exposure problems often discussed in IAQ talks?
    jerry
  • Douglas Hicks
    Douglas Hicks Member Posts: 69
    Don't forget wood gas.My house was built in 1890. When I did some remodling I found 3/8 black pipe. I found that there was a wood gas plant that supplied gas to homes and businesses. The house was remodeled in the early 50's and the gas lights were thrown out. My house was build w/gas and electric lights.
    Douglas Hicks
    General Fire Equipment Co of Eastern Oregon, Inc
  • Jeff_17
    You have all
    been very helpful. I know that the town I live in supplied the gas...
    I WONDERED mostly what made for the difference in the "Lighting" flames and the flames we NORMALLY see today burning in our boiler chambers or on our gas cooktops. I did not realize that the yellowish color was a result from a "cooler" flame. Gas lights in those days were "respected" and today, they are long gone with the Dead Men who were installing these lighting sources. Our home lies in a historic district and it remains virtually untouched from its 1903 beginning. If we open the house for house tours that our town wants to initiate, I thought it would be special to see one or two of these light fixtures "working" TEMORARILY....and of course with windows open.
  • Tom_35
    Tom_35 Member Posts: 265
    OK Tim,
    Give us the answer to the question of the day. I've often tried to get close to the fireplace of restaurants on cold days, but I'm guessing you're getting ready to change me.
    Tom A
    Steamhead Member Posts: 18,750
    Jeff, you might want to check
    with the Code authorities in your area. Many locales have outlawed the use of gas lighting. I remember reading that the Lovely Lane Methodist Church in Baltimore (first one in America, for you Methodists out there) originally had a spectacular celestial display in its ceiling that was lit by gas. During a recent restoration, they had to get special permission from the Code authorities to put it back into service.
    Consulting
  • Jeff_17
    This was only...
    a thought. Not sure if it will ever happen.
  • Constantin
    Constantin Member Posts: 3,796
    It is my understanding...
    ... that the soot from diesel engines, candles, and the like will have a somewhat oily consistency, whereas soot from gas flames impinging on cold surfaces will lead to a very fine soot that is a lot like black dust. Carbon black is used in everything from tires to newsprint.
    I can't remember how aldehydes form, yet I learned to smell for them when I was designing/testing the outdoor gas water heater. They're a sure sign that the combustion has gone to heck. If you can't smell the aldehydes, it's no gurantee that CO is not present... it just means that it won't be present in ridiculous amounts.
  • It has been my experience
    with decorative fireplaces in Hotels I have visited to find CO readings in the close proximity to the firepalces of 200 to 400 PPM. One in particular in North Carolina had over 600 PPM.
    I also check every room I stay in at hotels and motels for CO.
    That same hotel in North Carolina had a first floor room next to an alleyway that had the vents from several side wall vented water heaters exhausting into a confined outdoor area. My room had 25 to 30 PPM with all the windows shut. When i went outside and tested in the alley it was 500 PPM. I CHANGED HOTELS.
  • Bob Harper
    gas lights& logs
    Manufactured gas contains as much as 40% CO. This is why in the old days you could turn on the stove to asphyxiate someone. The color and pattern of the flame from a oight fixture burning mfd. gas are quite different from the same fixture burning NG or LPG. I found one old conversion boiler in Philly still set up to burn mfd. gas. It was pumping out ~1,600 ppm CO and the chimney was rotten. I guess this points out why more people didn't die back in the day or in this case: The houses leaked like a sieve. The Stack Effect flushed all the nasties out fast enough to keep from killing everyone.
    As for vente logs in restaurant fireplaces, this is a bad idea. I'm working on a case in Atlantic City with negative 27 Pascals of pressure. You can't hardly open the doors.Putting atmospherically vented appliances in commercial establishments with these huge exhaust only ventilation systems is really asking for it. I had another case in Wilmington, De. in a 4 star restaurant. The vented logs were installed in an old forge and vented really well horizontally out into the room until someone opened the front door. Then, they'd vent up the chimney for a moment. The chimney becomes the makeup air system for these buildings. BTW, ASHRAE 62.2-2003 would force builders to balance the houses including providing engineered makeup air where the house is less than 0.35ACH or as otherwise indicated by NFPA54 air requirements. If a builder claims his house leaks enough, 62.2 says he has to prove it with a blower door test. Now, if we could only agree on combustion spillage testing and Duct Blaster testing...
  • Greg_26
    Wow!
    At first I'm not sure if I believed that story. You actually tested the air in the room, the alley, AND changed hotels!?!? Then I recalled a woman I worked with years ago. Her ex-husband was a fireman. She said she hated going any place with him because no matter where they were all he would talk about was how unsafe everything was. I'll never forget the story she told me about an anniversary dinner they went on. During cocktails she said he went on and on about how many people would die in the restaurant if there was a fire. How romantic – “Your tables ready”. She ended up divorcing him because of it. Doesn't there come a point when you have to just live your life and take some reasonable precautions? There is no doubt that CO is dangerous but compared to a lot of things, I mean, millions of people use it every day and there are bound to be problems but that does not mean that you should change hotel rooms. How can you drive a car if you are worried about CO levels in your hotel room for one night? You are far, far, far more likely to die in your car, or even your tub for that matter.
    Hank
