What are the odds??

switches Fail on a brand new install aggghhhhh!!!
put in a 9 section 80 ser. w=m steamer sweeeet job, 2 mts later fire dept is there.....boiler totaly baked reading was 550* with the frie guys inrered gun, both the #11 switch and the 2m model 2 bothstuck in the open posision the floats were fine just the switches were no good the feeder never feed and it never shut down on low water. the back section cracked and had to replace all the seals in the hole boiler and the jacket, it was cooked, and a hole day for two men. WONDER whos going to pay THAT bill!!!!!. Fat chance of seeing a check in this life time......David

Comments



  • We've had a SLEW of (what we thought were) bad no.11 switches in 67s.

    On the ones we've had, I had to disassemble the 67s and "free up" the movement of the floats. It at first appeared to be the switches, but proved to be the floats themselves.

    For one customer, I had to install the whole float assembly from the old LWCO from the old boiler.

    I mentioned it to the supply house, and they just handed me a new float/no.11 switch assembly.... AND THAT ONE WAS BAD TOO.

    What will we do? Good old fashined tried and true products are failing us, making us look like idiots.
  • Dave Yates (PAH)
    Dave Yates (PAH) Member Posts: 2,162
    Positively weird timing

    We're having a slew of #67 problems too and it's been driving us nuts! Just the opposite - ours are sticking and causing flooding. Nothing can be found wrong with the end switches or the floats. No sediment - not a bit and this is a new installation. Grrrrrrrrrrrrrrrrrrrrrrr

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Glenn Harrison_2
    Glenn Harrison_2 Member Posts: 845
    Might I suggest...

    that you guys and anybody else who has any problems with a McDonnell & Miller porduct contact Greg Roder of M&M at greg_roder@fluids.ittind.com or 773-250-1314 of fax 773-267-0991.

    I know he wants to know about any problems anybody has with M&M products, and will do his absolute best to resolve the problem.
  • Man , that's a bad break

    I had an almost dry fire years ago on a new install when the 67 let the burner run with no water in it . About 3 minutes run time you get a funny smell from the new boiler when theres no water in it . We let it cool off for a looooong time and filled it while saying our Hail Mary's .

    After that incident we always turn the power on before we fill the boiler and make sure the LWCO works , at least for the 1st time . I hope the LWCO manufacturer gets involved and ponies up some cashola . These controls should not be bad right out of the box . Did you hang on to them ?
  • Al Gregory
    Al Gregory Member Posts: 260


    Watts made a great LWC I dont know why they stopped.
  • David Sutton_5
    David Sutton_5 Member Posts: 87
    Hi Ronjr

    Man that realy was a big bad thing, sweet lookin steamer too, i ALWAYS check the LWCO's on start up. been doin this thing to long to trust anything. well we will see what happens see ya ron....David