glen can you give me direction/ i wk for local gas utility/i had a cont install a in5 last jan i had water hammer problems/ add chemicals /slim boiler seemed to do trick now
2 fl rad spitting water and gurgles boiler goes off on pressure bef that rad gets hot ater next cycle it gets hot im having con come to look at it what dir should go never changed rad can it be pitch problem /can boiler be oversized and im pushing wet steam

Comments

  • PB48

    Is the radiator that spits water out the vent getting hot? I would immediately suspect that it is not pitched back towards the supply. What pressure are you running in this installation? Have you changed the vent? Lots of possible reasons for this happening. Let's see if we can narrow the possible ones down a bit. Let me know.

    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    www.burnham.com
  • pb48
    pb48 Member Posts: 20


    rad gets hot 2.5 cut out/ im using hoffman valves in rad/ rad noisy like its got water in it/change air val same cond
  • Check the pitch

    I would check the pitch on the radiator. Also turning down the pressure wouldn't be a bad idea either. Let me know what you find.

    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    www.burnham.com
  • pb48
    pb48 Member Posts: 20


    thanks glen should i go to 2lbs or less
  • Yes

    Most steam systems like working on lower pressures. The steam moves through the system more efficiently.