Convector Temp. from 1st to Last Unit

Neil_5
Member Posts: 179
Here is the system: gas fires water boiler, mono flow system with cast iron convectors, main line runs through the basement (not insulated) normal temp 65*. Rest of pipe run throught the house and garage (in wall). No insulation on the entire run of copper line.
Set the boiler temp to 200*, outside is 30. First two units are seeing 195*, the 4th and 5th units are seeing 155*, and the last 2 units are seeing 140*. If this normal, or a flow problem, or an insulation issue with the main copper line?
Taco 007 circulator, cold pressure: 12psi, warm pressure: 20 psi. No air in system.
Neil
Set the boiler temp to 200*, outside is 30. First two units are seeing 195*, the 4th and 5th units are seeing 155*, and the last 2 units are seeing 140*. If this normal, or a flow problem, or an insulation issue with the main copper line?
Taco 007 circulator, cold pressure: 12psi, warm pressure: 20 psi. No air in system.
Neil
0
Comments
-
need a lot more info-pipe sizes, btu output of convectors to design system. Have to work backwards to find the problem-could be not enough flow, wrong size venturi tees,insulation or you may have to "split the loop"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 947 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements