adding modine unit heater to steam system with radiators
mark_47
Member Posts: 1
I am considering adding a modine steam unit heater to a system with radiators. Main is pitched away from boiler with a return line looping back from end of line. How should i pipe unit heater (one or two pipe and with or without trap if two pipe
0
Comments
-
Two-pipe, no trap
Put a vent on the return side of the Modine, and run the return line into a wet return below the waterline.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0