Steam pressure and venting
Ray_2
Member Posts: 21
I have recently moved into a house with a one pipe steam heating system. In trying to be sure I get the most heat for the buck - I came accross the site- and have some questions
My pressure Trol is set as follows
Main= 5 psi Diff= 2 psi
I Have read a couple messages that say the pressure should be set around 2 psi. Should I turn mine down to 2psi? What are the pros / cons to doing this? What is the proper way to determine the pressure settings?
I have replaced all my radiator vents with Maid o Mist vents- size of vent depending on the location and size of the radiator.
I also have two valves in the basement on the pipes that I question their size and if they are properly located. The main pipe comes out of the boiler and splits 2 directions-23 feet to one side, 15 feet to the other, the pipe measures about 2 3/8 diameter. One radiator on the 15 foot side, 6 radiators on the 23 foot side. at their extents the pipes make a u-turn, reduce to 1 1/2 inch pipe, and make their way back toward the boiler. At the boiler both returns have a T. The top of the t has the valve(A Dole 1933),The bottom the the t's branch down then connect together and return to the boiler in a single pipe. I question whether the Dole 1933 valves are located properly? (at the end of the returns) Are they enough to vent the main? How will this effect my heating system if these vents are wrong / not working properly? Maid o mist has vents for mains - but they clearly are a bigger vent and I worry about to much venting, If possible? What is the proper vent for the end of the return / main
Thanks in advance for the help
Ray W
My pressure Trol is set as follows
Main= 5 psi Diff= 2 psi
I Have read a couple messages that say the pressure should be set around 2 psi. Should I turn mine down to 2psi? What are the pros / cons to doing this? What is the proper way to determine the pressure settings?
I have replaced all my radiator vents with Maid o Mist vents- size of vent depending on the location and size of the radiator.
I also have two valves in the basement on the pipes that I question their size and if they are properly located. The main pipe comes out of the boiler and splits 2 directions-23 feet to one side, 15 feet to the other, the pipe measures about 2 3/8 diameter. One radiator on the 15 foot side, 6 radiators on the 23 foot side. at their extents the pipes make a u-turn, reduce to 1 1/2 inch pipe, and make their way back toward the boiler. At the boiler both returns have a T. The top of the t has the valve(A Dole 1933),The bottom the the t's branch down then connect together and return to the boiler in a single pipe. I question whether the Dole 1933 valves are located properly? (at the end of the returns) Are they enough to vent the main? How will this effect my heating system if these vents are wrong / not working properly? Maid o mist has vents for mains - but they clearly are a bigger vent and I worry about to much venting, If possible? What is the proper vent for the end of the return / main
Thanks in advance for the help
Ray W
0
Comments
-
steam
Go to the books section of this site and order "We Got Steam Heat" and after that "The Lost Art of Steam Heating". If you have steam Heat you should have both of these books. They explain everything you should know as a homeowner about your system most importantly how and why it should properly work.0 -
Crank it down
Main-2 pounds. Differential- 1 pound. That's all you need.
Those Dole 1933 vents are really made for convectors, not steam mains. Vent the long main with two Gorton #1, Maid-o-Mist #1 or Hoffman #75 vents and the short one with just one of these vents. This will fill the mains in a hurry.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements