FAN LIMIT CONTROL
RICK_22
Member Posts: 2
wHAT SHOULD THE SETTINGS B FOR THE fAN CONTROL ON OIL FURNACE. I SET THE ON AT 150 AND OFF AT 110 AND LIMIT 200. ALSO ENCOUNTERD CALL EVERYTHING FROZEN IN OIL LINE UP TP NOZZLE, IS THEIR ANYTHING TO PUT IN TANK TO GET RID OF WATER.TANK WAS REAL LOW. ADDED 15 GAL OF KERO ,REPLACED FILTER AND NOZZLE AND FIRED UP /.
0
Comments
-
wHAT SHOULD THE SETTINGS B FOR THE fAN CONTROL ON OIL FURNACE. I SET THE ON AT 150 AND OFF AT 110 AND LIMIT 200. ALSO ENCOUNTERD CALL EVERYTHING FROZEN IN OIL LINE UP TP NOZZLE, IS THEIR ANYTHING TO PUT IN TANK TO GET RID OF WATER.TANK WAS REAL LOW. ADDED 15 GAL OF KERO ,REPLACED FILTER AND NOZZLE AND FIRED UP /.0 -
I set them at 200 limit, 140 fan on, 110 fan off. That seems to work well. I took some training through the PA Petroleum Association a while back and they suggested those settings, but if your system has an oversized furnace or fan or short duct runs, set it at 170 limit, 130 on, 90 off. Undersized furnace or fan or long duct runs set at 230 limit, 160 on, 130 off. I have never set them different than the first settings I listed with no problems.0 -
Those setting should be fine,
as to additives the trick is to start in October, not now! A dose with each delivery can save the customer beaucoup bucks and a lot of grief. IME, most are happy to do it once taught.
As to products the trick is once you start stay within the same product line, don't make cocktails in the tanks. Personally I have always liked these and based on experience, JMO: http://lincolnlaboratory.com/additives.shtml0 -
Why lower or raise the high
limit temperature? The high limit on a warm air furnace should not be above 200 degrees. A better way is to determine temperature rise across the furnace and then determine CFM to be able to control duct temperature. A good rule of thumb is to never have the blower running with a supply duct temp below 100 degrees (F)
Formula for CFM:
CFM = BTUh's (OUTPUT)divided by 1.08 x CHANGE IN AIR TEMP
EXAMPLE:
CFM = 120,000 BTU's divided by 1.08 x (130*-60*F)
CFM = 120,000 divided by 1.08 x 70
CFM = 120,000 divided by 75.6 = 1587 CFM0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements