hot water heat sizing....
kevin coppinger_4
Member Posts: 2,124
if HWBB tube sizing 20F delta T allows ABOUT 80K for 1", 40K for 3/4" ,and 15K for 1/2" , about what could I get out of 1 -3/8" tubing run???? I 'm doing a home run set up w/ panel rads....kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
What no HDS yet?
19,000BTU/hr at 1.9gpm, 6.5'of head per 100 feet of tube 4 fps
Bump to a 30° delta t for 29,000, at 2gpm 6.7' 4fps
hot rod