furnas on my one-line steam system

The furnace on my system does not run long enough to get the steam to second floor radiators. Pressuretrol is set at .05 bottom and thermostat anticipator set at high, about 9. What is my solution? No professionals found within 100 miles.

Comments

  • Steamhead
    Steamhead Member Posts: 17,425
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • ed wallace
    ed wallace Member Posts: 1,613
    boiler not heating

    is the differantial set for 1 on the little white wheel on pressuretrol whats the thermostat set for if its set at 65 boiler might not run long enough to heat 2nd floor
  • Dale
    Dale Member Posts: 1,317
    Diff.?

    What's the differential set at, should be 1.5#, little wheel inside the pa404a if that's what you have. I think your problem is air not getting out of the mains quick enough. You could also just have plugged rad vents or closed rad valves although the valve is pretty obvious. I would take a rad vent off upstairs and carefully see if air come out when the boiler is turned on.
  • Stephan
    Stephan Member Posts: 7
    2 nd floor problem

    I could write pages about what I did to fix problem like the one that you have. But all I could write is allready written in "The lost art of steam heating" by Dan Holohan.Believe me it will save you a lot of money. Good Luck. Stephan
This discussion has been closed.