Thermostatic Vents for Single Pipe Steam
Drod
Drod Member Posts: 59
In my quest to even out the heat in my house, I had the following interesting suggestion from Boilerpro. He wrote:
"They are just like TRV's except they install at the air vent on one pipe steam heaters. When the room reaches the temperature setting, the vent closes, slowing the rate that steam enters the radiator because it prevents more air from getting out of the radiator. When the boiler shuts off and the pressure in the system drops, air is brought in through a vacumn breaker and the radiator fills with air. Then when the boiler fires up the next cycle, the steam can't get in because the air can't get past the closed vent. This is how I understand they work. Take a look at the Danfoss Website... you can see some there. Installation is a matter of spinning off the old vent and installing the valve and new vent."
Since everything is working well on my system after several years of tweaking, venting, etc. (Thank you all), I appreciated his suggestion. But, I've been to several sites, including Danfoss, and I'm having trouble identifying exactly which items are the thermostatic vents for single pipe steam. Any suggestions?
Thanks,
DRod
  • DWood
    DWood Member Posts: 60
    Danfoss 1 Pipe Steam
    DRod
    Here's what you're looking for, let me know if you need a source.
    DWood
  • Drod
    Thanks, Perfect. If you can reccomend a source, that'd be great.
  • bb
    bb Member Posts: 99
    most plumbing and heating
    distributors should be able to get our 1 PS. Order Danfoss Code Nos.:
    013G8250 - Operator
    013G0140 - 1 PS Valve Body w/ Vacum Breaker
    013L8011 - Vent for 1 PS Valve.
    Any questions please call me @ 443-648-1205.
    Warm Regards,
    bb
  • John Shea
    John Shea Member Posts: 247
    What's a ballpark figure for one for the average consumer?
  • Evan J_4
    Evan J_4 Member Posts: 1
    Macon OPSK
    The Macon OPSK thermostatic valve radiator valve for one pipe steam can be ordered from www.StateSupply.com for $95. I installed one of these last year on a bedroom radiator that always overheated the room, and have been very happy with it.
  • Nelson R. Pardee
    Nelson R. Pardee Member Posts: 11
    Ballpark Figure
    I found the Danfoss online at a couple of places, but have not ordered from them: Webb Supply and Garnet Midwest. I also found the Danfoss locally for about $82 (including a Gorton vent), which is close to the cheapest cost I've found online.
  • Boiler Guy
    Boiler Guy Member Posts: 585
    H/well Braukman
    Any one familiar with this product. H/W does not include a vacum breaker does Danfoss?
  • Drod
    Which model for radiators covered
    All of my radiators have metal enclosures set around them. Which version do you suggest?
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    There are remote actuators
    Available for them, I believe.
    Boilerpro
  • bb
    bb Member Posts: 99
    Drod
    You can use a wall mounted operator and place it the sensor outside of the cabinet for this applicaiton. See the attached data sheet.
  • bb
    bb Member Posts: 99
    danfoss
    1 PS valves include vacum breaker. See our data sheet above
    bb
  • BillW@honeywell
    BillW@honeywell Member Posts: 1,099
    We make them too...
    Ours are Y100P1001, which includes the valve, and the steam/air vent. You can also use the T100 actuator, the T100B remote sensor or the T100F remote sensor. Check it out at http://hbctechlit.honeywell.com. Type in the numbers above, no charge and no password required. Available from any progessive steam/hydronic wholesaler.
  • Boiler Guy
    Bill
    That is the product number I have. However, when I read the enclosed literature it recommends adding a vacum breaker. Nowhere can I or my supplier find a device which is directly compatible with your valve. Any help would be appreciated.
  • BillW@honeywell
    Hi, Boiler Guy!
    We just make the valve, vent & thermostatic actuator. I think Danfoss builds their vac breaker into their valve. A seperate vac breaker should be available from a steam oriented wholesaler, but I don't have a brand name or number handy. Any ideas MadDog or Steamhead???
  • bb
    bb Member Posts: 99
    you are correct
    the Danfoss 1 PS does have a vacum breaker built in to the valve.
    bb