VECO SYSTEM
ED MOORE
Member Posts: 2
HELLO GENTLEMAN I JUST LOOKED AT A STEAM JOB THAT WAS A CLASSIC VECO SYSTEM EXACTLY AS LAID OUT IN THE LOST ART OF STEAM HEATING PAGES 255 256 MY QUESTION THERE WAS NO HARTFORD LOOP ON THIS JOB IS ONE NEEDED OR IS EQUALIZATION PROVIDED VIA THE RECEIVER REGULATOR AS I SUSPECT?????? THERE WAS NO CHECK VALVE IN THE RETURN
THANKS IN ADVANCE FOR ANY HELP
THANKS IN ADVANCE FOR ANY HELP
0
Comments
-
Every boiler
needs a Hartford loop and equalizer. Even on a VECO. How about taking some pics and posting them?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead,
How come the old Veco's did not have hartford loops and equilizers? I noticed on pag 256 of The Lost Art it shows a steam Veco system that looks as if it where pipied like a water boiler? Although, on page 255 there is a diagram where the boiler has an equilizer on the right and a reciever on left. Where these different install methods?
Also, every Veco system I have come across no longer has the reciever. How intricate is that part and why where they eliminated?
Attached is a picture of the new Steam boiler we just put in attached to a Veco System. (this is the one we talked about the other night)
Jamie
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Nice job dude
We see alot of old vapor systems still with original boiler...with no Hartford loop or equaliazer. Thes old pups have such a strapping steam chest that it could compensate for mssing elements like that. We still see alot of 3" and 4" header too..even on average-sized residential boilers. Today, with thse smaller faster, low water content boilers, Hartford loops, equalizers and good headers are vital . Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
VECO ANSWER
THANKS FOR YOUR HELP WILL BE DOING THIS SPRING LOVE TO TAKE PICTURES AND POST AGAIN THANKS!!!!!!!0 -
The Hartford Loop
had not come into general use when these systems were installed. This is why we don't see them on boilers from the 1920s and earlier.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements