uneven heat in one pipe system

I have a one-pipe steam system. All the vents are either Gorton type "C" main vents and the rest are all Gorton type "4" vents. All the main vents are in the upstairs of the house at the end of the mains. The downstairs has always been cold(er), so this winter (as we have a baby), I switched the vents and put the main vents down and the #4 vents up. The heat is much more even throughout the house, the boiler runs less, but there is now very slight hissing in some of the vents. Would it be better to leave the main vents at the end of the mains where they originally were and just get bigger vents for the big radiators downstairs, or leave the mains downstairs where they are now?? Thanks

Comments

  • Fred Harwood
    Fred Harwood Member Posts: 261
    vents

    Give it a try. Vents are inexpense. Your main vents at the end of the mains (near the drip to the wet return) should be Gorton #1 or larger, or even two #1s.
  • Deacon Shupp
    Deacon Shupp Member Posts: 2


    Thank you, I will try that.
  • Steamhead
    Steamhead Member Posts: 17,547
    Size your main vents properly

    and the system will be much easier to balance. Measure the length and diameter of each steam main- outside diameter is fine, subtract 1/4-inch from that to get the pipe size. If there's old insulation on the pipes, do not disturb it- carefully measure the outside diameter. Subtract 2-1/4 inches from that (this old insulation was almost always 1 inch thick) and that's likely your pipe size.

    With this info we can tell you what you need.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting