steam

shawn_5
shawn_5 Member Posts: 52
We have been to this job a bunch of times.The hose is 40 years old steam system alot of 2 inch black what is happening is the pipes start leaking not on the threads b=ut on the pipe any reason for this or is it common.

Comments

  • Al Letellier
    Al Letellier Member Posts: 781
    leaking steam

    Check the PH of the system water, Shawn. You're rotting out the mains with excessive acidity in the water. I've seen this quite often. The system has most likely had poor or no maintenance over the years, and bad vents mean a lot of new water and oxygen in the system, which will always lead to corrosion of one sort or another.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • clammy
    clammy Member Posts: 3,162
    insulation ?

    Are the mains that are rotting not insulated and how is the near boiler piping.I,ve ran into the bottoms of main leaking from excessive condensate in the uninsulated mains it groves the pipe from the excessive condensate flow usually shows up near the threads .In most cases i,ve run into the basements or crawl spaces where un insulated and pretty much as cold as out side at times .The homes usually heated very uneven but with very large homes there are wings that don,t even see the light .Good luck and follow al,s post also and check your water ph and while your at it why not give the boiler a water side clean drain the mud legs and such i know not many do it but it should be done peace clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • Steamhead
    Steamhead Member Posts: 17,380
    Another thing that can cause this

    is improper air venting. Insuffucient vent capacity can cause the CO2 in the air to mix with the condensate, turning it into carbonic acid.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • shawn_5
    shawn_5 Member Posts: 52


    also on all the radiators the vents are in the middle should they be at the top of the radiator also the breaking pipes are all around not just near the boiler