Is this a Hartford Loop

Jeff_44
Jeff_44 Member Posts: 94
Please forgive my non-digital photo, but after reading
Dan's book, I began to study the piping around my
boiler and can't quite figure if I have a true Hartford Loop.


Based on my drawing, can anyone help me?

Thanks, JC

Comments

  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688
    You're right.

    No true loop. The header is also incorrectly piped. You pipe to the system after you connect both boiler risers then drop into the equalizer. The Hartford loop typically is a tee in the equalizer 2-4" below low level mark, then drop to wet returns..Robert O'Connor/NJ
  • jbplumber
    jbplumber Member Posts: 89
    can not see u

    Jeff--can not seem to bring you up on screen.
  • Jeff_44
    Jeff_44 Member Posts: 94


    Thanks Robert,

    Since the piping is not correct, what problems may
    be associated with it? It's an old system that appears
    to be original to the house (65 years old). Even though
    it's old, it runs very even and quiet.

    Thanks,

    JC
  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688
    Jeff..

    Look to the left and click on the Library. At the bottom, then click on (or scroll down) to steam heating. I think you'll find you're answer there or if you have the manufacturers installation instructions available, this will show correct near boiler piping. If the system works as you say, the header mis-pipe may not be so critical, although installation of the loop is recommended..Robert O'Connor/NJ
  • Kal Row
    Kal Row Member Posts: 1,520
    te check valve is taking the place of the HFD loop...

    ie the purpose of the Hartford loop is to keep the boiler level from dropping down when the water level rises at the other end of the steam header in the basement – in your case the check valve is doing the same thing, you must have one clean system if it’s still working after all these years, as the checks tend to get sludged up, the Hartford loop has no moving parts to fail – but if it’s working great don’t mess with a thaaangg!!!
  • Maine doug
    Maine doug Member Posts: 47
    To the left is

  • Bill Nye_2
    Bill Nye_2 Member Posts: 538
    Jim

    Just wait................ it took a couple minutes to load on mine. And no, it doesn't look like you have a hartford loop
  • jbplumber
    jbplumber Member Posts: 89


    thanks Bill