Sucking Steam Vents and Clanging radiators
Tom Zydowsky
Member Posts: 8
Hi All,
I have a 15 year-old SlantFin single pipe steam bolier. Recently I've noticed that several of the my radiator steam vents begin to suck in air about 5 minutes after the boiler shuts down. Any thoughts on what's causing this?
Also, I have several radiators (not the ones that suck air) that produce a bell-like noise about 5-10 minutes after the boiler shuts down. Any ideas?
Are these events related?
Thanks,
Tom
I have a 15 year-old SlantFin single pipe steam bolier. Recently I've noticed that several of the my radiator steam vents begin to suck in air about 5 minutes after the boiler shuts down. Any thoughts on what's causing this?
Also, I have several radiators (not the ones that suck air) that produce a bell-like noise about 5-10 minutes after the boiler shuts down. Any ideas?
Are these events related?
Thanks,
Tom
0
Comments
-
since its happening after
the boiler shuts down, i'm wondering if the main vent(s) are not opening to break the vacuum..do you have main vents?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Yes. About three weeks ago I installed two #1 Gorton air eliminators on the front (45') main and one #1 on the rear (20') main. Before that I had one Hoffman #41 on the front and one Gorton #4 steam valve on the rear (left from the previous owner).
I checked the main vents and couldn't hear anything like the noise I hear from the rad vents. The rads are on opposite ends of the top floor in a two-story bldg and right above the main vents.
Thanks0 -
Check your steam pipes
if they are not insulated, steam will condense in them and cause a vacuum when the boiler shuts off. This will cause the vents to pull air in.
The bell-like sound is the cast-iron radiators contracting as they cool. It's normal- my hot-water radiators do the same thing.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Steam Lines
Steamhead,
I insulated my steam lines and will see if that helps.
Thanks to you and Gerry for suggesting ways to eliminate my vacuum problem.
Tom0 -
radiators sucking in air
Hi Tom,
It is normal for the one-pipe radiator vent to draw some air back into the system after the boiler shuts off. The old timers used to try to prevent that from happening when systems were fired with coal. The theory was, keep the system in a vacuum and the boiler could make steam at lower water temperatures as the coal fire died out at night. This doesn't work with automatic gas or oil fired burners, so we let the air back into the system during the off cycles.
The noise is probably as Steamhead describes, expansion noise.
Best regards, Pat0 -
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements