Riello Sooting Up In Buderus Boilers

Hi all, Just wanted to know if anyone has had a problem with Riello burners sooting/clogging up the end cone. I have a Buderus G-215-3. I have heard of this problems on other Buderus boilers with the same burner. The burners were all installed to factory specs. An efficiency test was done on all units when installed, and seemed to be running clean at the time of the test. A few months would go by and the burners would start to sputter and mis fire. After cleaning the end cone off and changing the nozzle all is well for a while??? Any help would be appreciated. Thanks!

Comments

  • Weezbo
    Weezbo Member Posts: 6,232
    it isnt set up correctly.

    instruments are the way to do it.who ever set it up for you would be the person to ask. i think it sounds like it isnt getting enough air.or there is alot of dust that has entered the burner thru the air shutter.
  • Ron Schroeder_3
    Ron Schroeder_3 Member Posts: 254


    Was it sooted on the tube or the slotted disk or both?

    Ron
  • dasplumber
    dasplumber Member Posts: 6
    Riello burner

    the soot was mostly on the slotted the disc and on the electrode tips . the burner was set up with combustion equipment.
  • dconnors
    dconnors Member Posts: 215
    the dead of winter

    If there is a time to find out whether there is enough combustion air, the dead of winter is it. As houses get closed up real tight, issues with combustion air and contaminates start to surface. Any recurring problem should be directed to Riello tech support.
  • Wayne M. Lawrence
    Wayne M. Lawrence Member Posts: 19
    Sooting Riello

    Was the over fire draft checked? I believe that boiler is a positive pressure unit. A high over fire draft condition will cause flame detachment. The face of the turbulator will be full of black coke deposits. You should have a good draft control,(I like the Field RC type) + set the damper to get +005- +01 pressure over fire. If an above ground fuel tank is used, Riello recomends an 80deg spray nozzle to off set a possible cold oil problem. Hope this helps.
  • Ron Schroeder_4
    Ron Schroeder_4 Member Posts: 46


    Which burner is it? F-3 or BF-3?

    Ron
  • dconnors
    dconnors Member Posts: 215
    Riello recommended?

    An 80 degree nozzle in a Buderus boiler? hmmmmm
  • Ron Schroeder_4
    Ron Schroeder_4 Member Posts: 46


    Hi Dave,

    A .5 Delavan 80 degree W nossle is the normal one for a Riello BF-3 in a 3 section G115-21.

    Ron