To much water in steam system
Brian_28
Member Posts: 2
I purchased a home built in 1901 with a two pipe steam system I recently had a new boiler installed because the old one had a crack in it . I am having a problem with to much water in the system, it has a auto water feeder which I have turned off, this was a problem even before the new boiler was installed. The sight glass is always full and some of the radiators dont work ,if I drain some of the water to proper level in sight glass then those radiators begin to work, but the next day the problem is back.
0
Comments
-
do you have wet return pipes?
if so it sounds like one may be clogged up..gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Yes I have two pipes that run along the basement wall at the floor so i am assuming that those are the wet returns. What would be the best way to unclog these returns.0 -
we usually replace them..
unless they were set up for cleaning its not easy, or clean..thats why we usually replace them.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Brian, was the feeder
replaced when the boiler was replaced? If not, it could be leaking. Also check the bypass hand valve if there is one, it might also be leaking.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
overfilling boiler
could it be that the boiler does not have as much water capacity as the old boiler and during off cycle the amount of condensate coming back is too much for the boiler volume capacity and it floods the boiler??0 -
loop seals
Make sure your wet returns are all under and does your system have drips on the mains into your wet returns .Do you know if the installer copied the original systems water line .I also think that alot of the newer boiler do have a larger steam rating and a smaller water holding cap.leading to feeders feeding while the boilers running and when all the condensate returns bang your flooded .I believe weil mc lean had issued a notice on this with a diagram for a a condensate resevare of some type peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements