Bunham PV88
tim smith
Member Posts: 2,835
Just saw this boiler on a site the other day, oil fired. Customer wants to know if it is convertible to gas. ?? anyone know. My literature does not show this boiler. It is probably 7 or 8 years old. I will check with Burnham later but thought someone might know here. Thanks Tim
0
Comments
-
RE: PV88
Tim,
This boiler was designed for and is intended to operate with oil. No testing of any sort has been done with gas burners on this boiler. If anyone chooses to equip this boiler with a gas burner, they must abide by the required controls and safety devices neccessary for gas equipment. Hope this helps.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
Thanks Glenn for the answer.
I would be concerned about the small firebox volume any way with gas in this boiler. Also this is only approved for oil, correct????0 -
Correct
It was designed, tested and certified for oil.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements