Main Steam Vents
Jamie_6
Member Posts: 710
Is it OK to tap the main steam vent in the side of the pipe?
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Yes
Use a minimum of 1/2" pipe, and tap at a slight angle to pitch the pipe back toward the main. Then elbow up to your vent.