wierd code on pinnacle

Gary Jansen_2
Member Posts: 26
My distributor called me wanting to know if I have ever seen a "NC" code on a new pinnacle boiler with the P125 board, not the old wha board. Calls to the man rep just got a shrug of the shoulders, call to Peerless were not returned as usual. Any ideas? Thanks, Gary
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=156&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=156&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
\"nc\"
is a temporary loss of neutral. It is an electrical issue with the wiring feeding the boiler. It usually happens when power is returned after a loss. There is power on the circuit board, but not a return leg. Like any computer, you may have to protect it with a surge protector, or most likly a UPS. If power outages are frequent in the area.
Hope this helps,
Chuck Shaw0 -
If a neutral
If it is a neutral problem make sure the power feed goes only from the panel to the boiler. I have seen shared neutrals in old basements cause alot of headaches.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 944 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements