sizing mainline air valves
dave_43
Member Posts: 9
I have two loops - loop A is 100' of 5" iron pipe and 100' of 4" iron. Loop B is 40'of 5" iron and 168' of 4" iron. Currently each loop has one Gorton #2 air eliminator. It seems like the individual radiators on the final risers are doing the bulk of the venting. As a result, the air valves frequently get wet and slow and the radiators do not heat consistantly. How many air eliminators should each mainline loop have? Thank you Dave
0
Comments
-
Stay with the Gorton #2
use 5 of these vents on main A and 4 on main B. This should allow the air to vent out of the mains in about a minute, and the end radiators will heat up much faster.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0