sucking steam rad
Frank S_2
Member Posts: 1
I went on a call today where the customer was complaining of a lack of heat and water hammer, or in his words "like someone is banging the pipes with a hammer" Boiler replaced 4 months ago. Aside from the atrocious near boiler piping....bullhead tee into the equalizer and main, 12" nipple on the hartford loop. I have 1 rad that actually sucks a match out when I take the air vent off! Any idea what I should look for as the cause of that problem?? Thank you in advance for your knowledge.
Frank
Frank
0
Comments
-
Wet Steam
maybe the result of that bad near-boiler piping. Or a pipe slightly off-pitch near the rad, holding just enough water to condense the incoming steam.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0