OK to drip riser with 17C trap?

brian_27
brian_27 Member Posts: 7
We're buttoning up our kitchen renovation, the pipefitters finished reinstalling risers and returns through kitchen walls to upstairs radiators. They were unable to get one of the horizontal runs to a riser sloped correctly, and I've got water stacking in the riser. Is it OK to use a 17C thermostatic trap to drip that riser (right at the elbow where it heads up into the wall)? I'm thinking a 3/4" 17C.

THANKS

Brian

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    You would have to

    use a cooling leg before the trap.
    Retired and loving it.
  • brian_27
    brian_27 Member Posts: 7


    thanks for the reply - if I may - the cooling leg would be required for an end-of-main drip, as I understand it. My situation is I have a vertical riser that you can hear the water boiling inside (3/4", feeding two small 2ft. tall 10 column cast radiators). The riser comes off the main at not quite 45 degrees (fitters did not get it quite right), so when it goes horizontal the end of the horizontal run, before it turns up into the wall, is lower than the beginning of the horizontal run, preventing the condensate from draining back into the main and getting pushed out the F&T (see attached). I'm thinking of putting the thermostatic trap where it turns up, the condensate would drain out the trap after each cycle and then steam would go up the riser at startup (after pushing a little more condensate out from the steam hitting the cool riser. Neither radiator is heating all the from top to bottom, new trap elements.

    THANKS

    Brian
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    It might work

    the thermostatic trap needs a 10- 15-degree drop in temperature to open, though. That's what the cooling leg is for.
    Retired and loving it.
  • Steamhead
    Steamhead Member Posts: 17,375
    Brian, what are you dripping the riser into?

    > the thermostatic trap needs a 10- 15-degree drop

    > in temperature to open, though. That's what the

    > cooling leg is for.





    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steamhead
    Steamhead Member Posts: 17,375
    Brian, what are you dripping the riser into?

    If the return line you will connect the drip to is below the boiler's water level, you don't need a trap. The water standing in the return will "seal" the drip so no steam will enter it.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • brian_27
    brian_27 Member Posts: 7


    Dan and Steamhead thanks for replying.

    Dan: I'm not sure I need the trap to open during the heating cycle, the pipe is insulated, I want it to drain after heating cycle and at startup.

    Steamhead: this would be dripped into the dry return.

    I love steam heat but this hammer is absolutely driving me insane!

    Brian
  • Steamhead
    Steamhead Member Posts: 17,375
    OK, you'll need the trap

    and it must be ready to drain any time condensate reaches it. That's why you need the cooling leg. Or, use a float trap that doesn't depend on cooling to open.